Hi I am a little confuse on how to use to NEC rules for transformer calculations. ...
... On your 2nd example, I am of the opinion that you can not use a #2, with a 115 amp rating, on your 125 amp breaker. Although the Code allows the "next size up" the conductor must be sized for the load and there is nothing to prevent the load reaching 125 amps.
ice:
That was the "in my opinion"
I think it's a fine line. IF you have a calculated load then I see no problem using 240.4(B).
In his case we have the transformer with unknown load. The 125% rule is for the protection of the transformer. In this situation with an "unknown" load there is nothing to keep the #2 from being loaded beyond it's ampacity.