I am working on a project that is getting a little over my head in knowledge and could use some help!!!
We have a 50KVA dry type transformer feeding a very large 330VDC Power Supply(Ametek SGE 330/91E-01A)
The customer is asking for the In-rush current and current consumption for the supply to the transformer, and I am not positive how calculate this?
Line side = 600VAC, 3-phase
Load side = 480VAC, 3-phase. This feeds the 330VDC Power supply which has a max input current of 73FLA .
Here are links for the power supply
WEBSITE:
http://www.signaltestinc.com/product-p/sga 330-91.htm
DATA SHEET
http://www.signaltestinc.com/v/vspfiles/assets/datasheet/Sorensen_SG_Datasheet.pdf
I found this formula for the breaker size of the line side, but not seeing how to calculate the in-rush current and current consumption
Amps for line side of 3-ph XFMR = Transformer KVA / (Transformer Primary Volts * 1.73)
Amps for line side of 3-ph XFMR = 50KVA / (600VAC * 1.73) = 48.17amps
for the circuit breaker sizing, I got 48.17Amps * 1.25 = 60.21amps
will a 60 amp service be enough for this?
how do i calculate the in-rush and current consumption for the line side of the transformer?
Thanks!
Eric
We have a 50KVA dry type transformer feeding a very large 330VDC Power Supply(Ametek SGE 330/91E-01A)
The customer is asking for the In-rush current and current consumption for the supply to the transformer, and I am not positive how calculate this?
Line side = 600VAC, 3-phase
Load side = 480VAC, 3-phase. This feeds the 330VDC Power supply which has a max input current of 73FLA .
Here are links for the power supply
WEBSITE:
http://www.signaltestinc.com/product-p/sga 330-91.htm
DATA SHEET
http://www.signaltestinc.com/v/vspfiles/assets/datasheet/Sorensen_SG_Datasheet.pdf
I found this formula for the breaker size of the line side, but not seeing how to calculate the in-rush current and current consumption
Amps for line side of 3-ph XFMR = Transformer KVA / (Transformer Primary Volts * 1.73)
Amps for line side of 3-ph XFMR = 50KVA / (600VAC * 1.73) = 48.17amps
for the circuit breaker sizing, I got 48.17Amps * 1.25 = 60.21amps
will a 60 amp service be enough for this?
how do i calculate the in-rush and current consumption for the line side of the transformer?
Thanks!
Eric