zog
Senior Member
- Location
- Charlotte, NC
kingpb said:I agree that testing the oil can determine many things, but to fully analyze the transformer, isn't it necessary to check all the failure modes, which, includes mechanical, electrical, and dielectric; both internal and external.
Looking at the oil only, may give some indication of the trouble ahead, and this may be enough by itself to make a determination on whether to replace immediately. However, say the decision was that based on the oil test it could last a while longer. Then, unexpectedly the transformer fails and it is because the whole transfomer wasn't tested, of which the other tests would have given a better understanding of the actual situation.
Based on this, oil tests alone may lead you to a conclusion that gives a false sense of security, which ultimately could lead to a unscheduled and undesired outage.
there is a big difference between a regular oil analysis and a DGA oil analysis, a DGA analysis tells you the type of problem and to what degree it occured by looking at the presense and levels of 9 different gasses, all of which are indictitive of different problems.
Yes ideally you would do a full barrage of tests as I stated in my first post but in thos case I think it would be a waste of money, if the DGA sample is within all the ANSI limits, then I would recommend a full set of tets before saying this unit is good, but I suspect the DGA levels will just confirm what seems to be obvious, this unit is toast.