Transformer secondaries

Status
Not open for further replies.

nickelec

Senior Member
Location
US
I have a question I think o know the answer to but just need verification. I have a transformer 277/480 primary and 110/208 secondary feeding a set of the panels I planned to come off the transformer into a troug/wire way. And feed 3 panels via taps. These Feeders would be less then 10' but I think that I need to hit a disconnect first then the wireway if I'm Correct. 240.21 (c) (4)? Or is it ok to to hit the trough and tap the feeder with out a disconnect before

Sent from my SM-G950U using Tapatalk
 

ron

Senior Member
A lot will have to do with how the transformer primary protection is sized? 125% or higher than the FLA or are you good with "primary only protection" per Table 450.3(B)?
 

nickelec

Senior Member
Location
US
A lot will have to do with how the transformer primary protection is sized? 125% or higher than the FLA or are you good with "primary only protection" per Table 450.3(B)?
I'm not that great at remembering formulas but how do I find the Max fla on the secondary side of a 75 kva transformer being fed via a 277/480 100 amp breaker?

Sent from my SM-G950U using Tapatalk
 

tw1156

Senior Member
Location
Texas
75,000VA / (480V x 1.73) = ~91A
75,000VA / (208V x 1.73) = ~209A

KVA remains the same on both sides of the equation.
 

Smart $

Esteemed Member
Location
Ohio
You have to run conductors all the way from transformer terminals to each panel's lugs. A transformer secondary conductor is considered a tap itself, so you cannot tap a tap.
 

nickelec

Senior Member
Location
US
Ty very much I was not aware , again I don't do many transformers

Sent from my SM-G950U using Tapatalk
 

nickelec

Senior Member
Location
US
You have to run conductors all the way from transformer terminals to each panel's lugs. A transformer secondary conductor is considered a tap itself, so you cannot tap a tap.
So it would be more practical to hit a disconnect then the trough so the load side of the disconnect aren't considerd taps anymore?

Sent from my SM-G950U using Tapatalk
 

nickelec

Senior Member
Location
US
You have to run conductors all the way from transformer terminals to each panel's lugs. A transformer secondary conductor is considered a tap itself, so you cannot tap a tap.
How did you come up with the fact that secondaries are a tap is it somewhere in nec or just experience in doing g this before

Sent from my SM-G950U using Tapatalk
 

nickelec

Senior Member
Location
US
secondary conductors must be terminated in a single circuit breaker or set of fuses.* Does this go for any length of conductors, basically saying it's never ok to install the setup I'm looking to without hitting a disconnect first not necessarily an OCPD?

Sent from my SM-G950U using Tapatalk
 

Smart $

Esteemed Member
Location
Ohio
So it would be more practical to hit a disconnect then the trough so the load side of the disconnect aren't considerd taps anymore?
Do you plan on your panels having a main circuit breaker (MCB) or just main lugs only (MLO)?
You should only need a [fused] disconnect switch if your panels are MLO.

How did you come up with the fact that secondaries are a tap is it somewhere in nec or just experience in doing g this before
The fact the section is in 240.21 is a clue... and I do have a fair amount experience. :blink:

secondary conductors must be terminated in a single circuit breaker or set of fuses.* Does this go for any length of conductors, basically saying it's never ok to install the setup I'm looking to without hitting a disconnect first not necessarily an OCPD?
There are a only a few, relatively rare cases where your secondary conductors can supply a load with no OCPD, or connect to multiple OCPD's. Note the single OCPD per secondary conductor is per set and you can run more than one set.... which is why I'm saying run one set to each MCB panel.
 

nickelec

Senior Member
Location
US
Do you plan on your panels having a main circuit breaker (MCB) or just main lugs only (MLO)?
You should only need a [fused] disconnect switch if your panels are MLO.


The fact the section is in 240.21 is a clue... and I do have a fair amount experience. :blink:


There are a only a few, relatively rare cases where your secondary conductors can supply a load with no OCPD, or connect to multiple OCPD's. Note the single OCPD per secondary conductor is per set and you can run more than one set.... which is why I'm saying run one set to each MCB panel.
I planned on using MCB panels but like you said earlier even if I use MCB panels I would need to run 3 sets from the transformer. Or run one set to a fused disconnect then MLO panels Wich I think is the best way to go.

Sent from my SM-G950U using Tapatalk
 

nickelec

Senior Member
Location
US
I planned on using MCB panels but like you said earlier even if I use MCB panels I would need to run 3 sets from the transformer. Or run one set to a fused disconnect then MLO panels Wich I think is the best way to go.

Sent from my SM-G950U using Tapatalk
So transformer, 200a fused Disconnect​, trough, 3 MLO panels . Is it permitted to tap after that fused disconnect? Or , are those conductors considered a tap as well?

Sent from my SM-G950U using Tapatalk
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
So transformer, 200a fused Disconnect​, trough, 3 MLO panels . Is it permitted to tap after that fused disconnect? Or , are those conductors considered a tap as well?

Sent from my SM-G950U using Tapatalk
What size wire are you running to the panels?

Unless you are protecting wires at more than their allowed ampacity at the start of a circuit you do not have a tap.
 

nickelec

Senior Member
Location
US
What size wire are you running to the panels?

Unless you are protecting wires at more than their allowed ampacity at the start of a circuit you do not have a tap.
My partners orgianal thought was to come off the transformer with a set of 3/0 to a trough then tap 3 times to feed 3 200amp main breaker panels. I want to come off the transformer to a 200 amp disconnect then feed 3 MLO panels. Keep in mind the existing panels are old feeding lighting and general receptacles. Currently fed via a 200amp feed.

Sent from my SM-G950U using Tapatalk
 

nickelec

Senior Member
Location
US
What size wire are you running to the panels?

Unless you are protecting wires at more than their allowed ampacity at the start of a circuit you do not have a tap.
Where does the circuit start at the primary ocpd or at the lugs on the secondary

Sent from my SM-G950U using Tapatalk
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
My partners orgianal thought was to come off the transformer with a set of 3/0 to a trough then tap 3 times to feed 3 200amp main breaker panels. I want to come off the transformer to a 200 amp disconnect then feed 3 MLO panels. Keep in mind the existing panels are old feeding lighting and general receptacles. Currently fed via a 200amp feed.

Sent from my SM-G950U using Tapatalk
If you have 200A wire coming off of your fused disconnect going to a trough and 200A wire going to each panel you don't have a tap, you have a splice.
 

ActionDave

Chief Moderator
Staff member
Location
Durango, CO, 10 h 20 min from the winged horses.
Occupation
Licensed Electrician
Where does the circuit start at the primary ocpd or at the lugs on the secondary

Sent from my SM-G950U using Tapatalk

It starts at the load side of your first disconnect on the secondary, until then you don't have any protection for the secondary conductors which is why you have to use the tap rules. A tap has a limited definition in the NEC and is not simply another word for splicing big wires.
 

Smart $

Esteemed Member
Location
Ohio
I planned on using MCB panels but like you said earlier even if I use MCB panels I would need to run 3 sets from the transformer. Or run one set to a fused disconnect then MLO panels Wich I think is the best way to go.
So you run three sets of 200A conductors... what is the big deal? You would have to use 200A conductors from trough to panel main in your "tap a tap" scenario anyway.

And if you used one fused disconnect, are you going to run 400-600A conductor set on both line and load side? What did you gain? You still plan on tapping this feeder with 200A conductors to each panel.

What are you gaining? You said it is all less than 10'. I don't know if I'd even bother with a trough. Just run three conduits from transformer, one to each panel.
 