Yes. Is that an issue?Like this?
View attachment 2563756
I'm specifically asking about keeping their c same rule and only making a change that would allow it to be used on Flush mount panels as well as Surface mount. Surface mount is all it allows for on 312.5cIf you read this entire thread, you find that the intent of the code is to contain an arc blast (I was not aware of that - I assumed it had to do with water entry). The arc blast concern would also apply to a flush mounted panel. In my own home, an interior flush mount panel was installed with all of NM stuffed through one big knock out in the top - no clamps and no duct seal. Doesn't this present the same problem that the code was trying to prevent with 312?
I want to see the data the CMP used in determining that a resi 120/240 meter combo or load center has a potential high enough arc blast that there is a difference from 12 romexes in a 2in nipple or shorter than 18” pvc nipple; compared to 1 or 2 romexes in a plastic nm connector.
Now lets not get that extremeIll turn in my license and join the plumbers.
We were told at an IAEI continuing education class about five years ago that NM cable should never feed into say a pancake box for a wall mounted luminare. Reason given was this is a damp location so NM cable is not approved for damp location. Told us to use UF cable. So appears that you should never run NM cable to outdoor panels.This has never ever been an issue for me.
And with a strict reading of the code, as long as the nipple does not exceeded 24”, no derating is required.
And while raceways outdoors are considered a wet location, romex has been fed into exterior mounted panels for as long as romex has existed.
The Code is great, but it’s not the Holy Bible.
In NorCal, I have done around 200 panel changes in 20+ years and I, nor any of the contractors I’ve worked for would have done or allowed work like the pics you’ve shown. I would say looking at those pics, those were not ‘electricians’; those were just ‘installers’-no real knowledge of code or building reqs or best practice. Hopefully, those pics are from inspectors who did their jobs and caught it and made them fix it.Not securing cable to the enclosure is just one of the issues with a rear entry of an exterior, surface mounted panel. It can be done in a satisfactory, if not an entirely code compliant fashion. However of the many hundreds that I have seen it was done satisfactorily fewer than five times.
The typical LA County residential electrician isn't interested in code compliance... mostly because they don't know any code. The cable comes through a big hole or a bunch of little holes. Sometimes there's fittings and sometimes not. The panel enclosure is mounted over a gutted flush panel or just a big hole in the stucco. Quite often there are splices behind the new enclosure. The finishing touch is to caulk around the top and sides of the surface mounted enclosure. Once the sun dries the caulk to a brittle ribbon, water is able to get in the wall.
Having read this thread I see that many of you are okay with a 2" nipple. That could work. The rub is that it takes an extra inspection to see that the wall has been restored and the nipple will be sealed. Did I indicate that it is just one extra inspection...well let me mention the lath inspection prior to stucco and then you provide a picture of the stucco patch.
So in LA County rear entry is not pemitted. I suppose that if you talk to the inspector and arrange the extra inspections, it could happen. But trying to control that with a hundred panel upgrades each day doesn't work. So no, if it comes down to being picky to put a stop what you see in the pictures....so be it.
View attachment 2564155
View attachment 2564156
View attachment 2564157
View attachment 2564158