I went to table 300.5 column 4. I’m just seeing if I’m missing anything but it’s pretty clear. Not sure if there is anything else. I’m just curious I’m running a 60 amp circuit to a shed and was going to install direct burial cable. I was wondering can I go 12” if I have that circuit on a 2 pole 60 amp gfci breaker?
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
No, the 12" depth is only for a GFCI-protected 120v circuit, 20a max.

For the minimum depth of 6", you need RGS conduit, or a 2" concrete cover.
 

Rock86

Senior Member
Location
new york
Occupation
Electrical Engineer / Electrician
Be careful with your wording. It sounds like you are running a FEEDER not a branch circuit. Also your circuit would be rated 240V. Consider if you need the 60A
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I went to table 300.5 column 4. I’m just seeing if I’m missing anything but it’s pretty clear. Not sure if there is anything else. I’m just curious I’m running a 60 amp circuit to a shed and was going to install direct burial cable. I was wondering can I go 12” if I have that circuit on a 2 pole 60 amp gfci breaker?
You'll need to go down a minimum of 24" to the top of the direct burial conductors.
 