JFletcher
- Williamsburg, VA
Got a call end of yesterday for 3 rooms w/o power at a hotel. By their room numbers, they are all on top of one another. I'm presuming they were initially wired in a riser setup using a common conduit for the home runs.
Scooted by for a quick moment to take a look. All 3 1p 20A breakers were tripped in rooms 408, 508, and 608 and immediately trip back when reset. My thought is that something shorted in the common (riser) conduit taking out everything. I didnt have time to investigate further and asked maintenance to move all of the stuff out of the way of the panels and wire gutters below.
Aside from unlanding the ungrounded conductors from the breakers in question and testing continuity between them (should be none, melted together wire would show continuity), what/where else might I look for problems? This place was built ~40 years ago. Is there any failure point that would be more likely than another, say the j-box, receptacle or light switch where they first come up in the riser? I'm thinking that all 3 circuits failed in the same place...why they might have failed is another matter.