Two 20A GFI breaker circs (separate Neutrals) in 12" bury conduit.

James L

Senior Member
Location
Kansas Cty, Mo, USA
Occupation
Electrician
IMO, a multiwire branch circuit is not 240v. A multiwire branch circuit can be considered 2 120V circuits. The table doesn't state the voltage in the conduit. It mention residential branch circuit 120v or less.
I don't see any way 1 circuit can be counted as 2

It's "multi wire branch circuit"

The plural is on "wires", but "circuit" is in the singular.

If you have load on both hots, there is hot-to-hot voltage. That makes it one circuit
 

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Try 210.4(A): Branch circuits recognized by this article shall be permitted as multiwre circuits. A multiwire circuit shall be permitted to be considered as multiple circuits. Except as permitted in 300.3(B)(4), all conductors of a multiwire branch circuit shall originate from the equipment containing the
branch-circuit overcurrent protective device or protective devices.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
In the particular context at issue for the OP, 225.30 says "For the purposes of this section, a multiwire branch circuit shall be considered a single circuit."
 

wwhitney

Senior Member
Location
Berkeley, CA
Occupation
Retired
In the particular context at issue for the OP, 225.30 says "For the purposes of this section, a multiwire branch circuit shall be considered a single circuit."
Nice, that supports the idea that an MWBC can be simultaneously one circuit for the purposes of applying 225.30, and two circuits for the purposes of applying 300.5.

Cheers, Wayne
 