Re: Two dedicated 20 AMP Circuits...
Back to Charlie's response. (Don't know where Allen was on that one.)
The fact that 2 different sized OCPD feed these two circuits in a MWBC is not that uncommon. As long as the neutral is sized to the largest return current. (I wouldn't suggest larger than 15 and 20 Amps, but that is my suggestion).
Even if you were max'd out on both circuits (12A and 16A) your return current is only 4A.
Back to Charlie's response. (Don't know where Allen was on that one.)
The fact that 2 different sized OCPD feed these two circuits in a MWBC is not that uncommon. As long as the neutral is sized to the largest return current. (I wouldn't suggest larger than 15 and 20 Amps, but that is my suggestion).
Even if you were max'd out on both circuits (12A and 16A) your return current is only 4A.