I don't believe "dedicated" is in there. Pretty sure NEC does have definition for "Branch circuit, individual".No book to look up dedicated, but to me it should pass as you are controlling the load/s of a function not multiple openings where anything could be plugged in.
I don't believe "dedicated" is in there. Pretty sure NEC does have definition for "Branch circuit, individual".
If you supplied two different utilization equipment from an "individual branch circuit" you don't meet that definition even if you have interlocking methods, IMO. But that may not mean your load calculation on service or feeder has to include both loads either.