And???:huh:
Is the charger 120V or 208V
The charger is a Tesla HPWC. It can run at 208V.
And???:huh:
Is the charger 120V or 208V
If it's not a simple "ok" to tap the existing feed, I will go down the road of using the main panel and reimbursing the HOA for usage.
30+ years ago the family lived up in a double. One night breakers starting tripping. Old house...no AC. After the Third trip to the Basement I started looking around. Found 3 different zip cords daisy chained from our washer recep across the Basement and up a common cold air duct. Excuses from my neighbor about mistake with payment and they just wanted to keep the fish tank running.Yeah they definitely don't want metered and unmetered wires together. I had a call years ago with the utility and property owner for theft of service. Meter bank just like that. One tenant meter was shut off, so someone paralleled #12's from one breaker to theirs. Free electricityWell, not free to the other guy.
Double tapping the load side of the meter for a 50A sub would work too, no ??
I will post the same picture here of the panel. So the consensus is that even though when I turn on all appliances I measure only 50 amp load, the panel is "full" and cannot spare a 50 amp feeder, correct?
Thanks for all the input everyone, I really appreciate it.
http://i63.tinypic.com/307vkw2.jpg
If it's not a simple "ok" to tap the existing feed, I will go down the road of using the main panel and reimbursing the HOA for usage. I was asking this question here originally because it would be much easier politically to use my own meter, if possible. I also asked because I received conflicting info from multiple electricians, all with the same certainty.
It seems the answer here is that is in fact not possible to use my meter.
And also for my charging station, it will use 208v @ 40amp with a 50 amp breaker.
Thanks!
Double tapping the load side of the meter for a 50A sub would work too, no ??
Tapping the feeder to your dwelling is very doable NEC wise. Tapping right at the meter center you do need to consider that the breaker is going to only be rated for one conductor per lug to land at it - so you will be making that tap in some other device and not in the breaker lugs if you want to do it properly. Another consideration is whether the wireways of the meter center have room for your added conductors and/or any tap devices. NEC does have rules on how full you can fill those spaces with conductors.Isn't that what I've been asking is possible?
I'm not clear on whether or not the load calculations necessary depend on the feeder going to the meter, or the breaker set in the apartment itself, or the actual load of the items in the apartment.
Thanks!
The charger is a Tesla HPWC. It can run at 208V.
Do you know the data name plate, FLA, watts, VA, rating at 208V for the charger? When charger is connected to the car, charging the batteries, how long does it take to full charge the batteries? More than 3 hours? When is the charging taking place? Anytime the car is parked in its' parking space? At the end of the day? Other?
EDIT:
mk23169 said:
Post #19
And also for my charging station, it will use 208v @ 40amp with a 50 amp breaker.
Is that the actual FLA for the charger? 40 amp @ 208V?
The charger is has a load selector so I can be programmed depending on the circuit is connected to.
If the load calculation shows I can only spare 40 Amp it will charge at 32A, if I can spare 50 amp it will charge at 40 and so on.
Does that answer your question?
https://www.tesla.com/sites/default...nstallation_manual_80A_en_US.pdf?201612081439
Here is a product that I have wanted to try for this specific situation but haven’t had a chance to yet.
https://youtu.be/eWm7rfxQZyc
It’s specifically for condos... the 100 amp service goes through this unit and then back.. the unit monitors the amount of power being used and allows you to charge your EV safely and within your existing service.
Ditto to all that. Can't even see his feeders, maybe in the wall. The OP hasn't answered any questions about the board or getting to where it will be located. Maybe he's on the condo boardWe understand how it's wired and what you show is just to illustrate that. In a real installation it would be very unusual to find enough slack in the existing feeder to be able to do it that way. In all likelihood, the EC will have to remove the feeder from the meter stack and replace it with a long enough cable to reach your unit. Hopefully your unit can be located within a distance where the original feeder will reach it, otherwise that will have to be spliced requiring yet another box to be mounted somewhere. In my experience meter rooms are rarely that neat and uncluttered.
Also, knowing what I know of condo boards, it would take an act of Congress to get them to allow something like that, no less "personal" EV charging stations. If they allow one person to do it they have to allow everybody to do it. Then how do you get the wiring out to each parking space?
-Hal
... Maybe he's on the condo board![]()