GerryB
- woodbridge, ct. USA
I have a code question here came up because of the supply chain issue. We have a new 7 unit apartment building requiring 8 meters. An eight gang meter bank with a main etc is at least 12 months out. The utility will allow two risers and two 4 gang meter enclosures. (One service drop from the pole). A breaker enclosure will be installed below each meter to feed the units and house meter. Do you need a main disconnect for the eight meters (or maybe a disco on each section, so 2 disconnects to shut the entire building).
The only leeway I see is 230.71(B) where it mentions "each set" of service entrance conductors, and 230.40 exception 1. which mentions "one set of service entrance conductors for each service".
I see it as not really two services but that is the argument. Thanks, we are on the 2020 code.