Is it permissible to wire the detached garage of a single family dwelling with Type NM cable (ref 334.10)?
We run NM in garages all the time here. What is the code reference?wbalsam1 said:I agree. It's a violation if the garage is detached.
iaov said:We run NM in garages all the time here. What is the code reference?![]()
Thank you.:smile:wbalsam1 said:334.10(3) covers detached garages.
ultramegabob said:is it attached if you string up a clothes line?![]()
four said:J-Box in Hot tub says Equipment ground needs to be the same size as hots.
stickboy1375 said:They need to stop that....
peter d said:Sounds like a familiar topic.![]()
The real question is if that manufacturers instruction is part of the listing and labeling.
wbalsam1 said:I agree. It's a violation if the garage is detached.
grant said:334.10 (3) allows the use of romex in a Type V structure with the exceptions listed in 334.12. Item (1) of 334.12 allows for the Type V structure to be applied and I see nothing in the balance of 334.12 that would keep you from using romex in a detached residential garage. Type V consturction is basic stick construction with a 1 hour rating. If the garage interior is covered with drywall there should be no problem. I also think there are Type V structures that are unprotected wood frame construction in which case the areas where the romex was installed would need at least a covering with a 15-min fire rating per 334.10(3).
grant said:Basically I can see no real difference between attached and detached or how the romex is protected.