dan123

Member
I ran regular romex 12 2 wire to my garage in PVC conduit. My town inspector told me I had to use UF wire. My electician friends disagree and tell me it should have passed. Can anyone tell me who is correct :confused:
 

iwire

Moderator
Staff member
Location
Massachusetts
Running NM underground even in conduit is a violation of 300.5(D)(5).

Conductors or cables underground must be listed for wet locations.
 

480sparky

Senior Member
Location
Iowegia
iwire said:
Of course.....but that is not what you said and if someone answered THHN on a test about wet location they would fail. :)

I hang my head in shame. I will also tear a small piece off my license now. :cool:
 

dan123

Member
Thank You

Thank You

Thank you for your replies. I have the 12 2 UF wire. I heard its hard to pull. I have 1 1/2 inch pvc. Someone told me to put vegitable oil on to help it along its way. What do you think:-?
 

iwire

Moderator
Staff member
Location
Massachusetts
I hang my head in shame. I will also tear a small piece off my license now. :cool:

As you should...:D


You did notice I had my 'wink' ;) on when I commented.

I know you know the difference between THWN and THHN.:cool:

Seriously though if I am ordering expensive copper and I need THWN you can bet I write THWN on the order. :)
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Dan, they make pulling lubrication specifically for the purpose of ......"pulling wire". Try it, it is not that expensive.
 

iwire

Moderator
Staff member
Location
Massachusetts
dan123 said:
Someone told me to put vegitable oil on to help it along its way.

I am closing this thread, in accordance with the Forum Rules.