Would like to get a clear answer on concrete encased electrodes ( UFER Ground) as the sole electrode in a system.
NEC 250.52 States that you can use a Piece of rebar 20’ or more and minimum of ½” diameter or 20’ of “bare copper conductor not smaller than 4 AWG” as the “Electrode”. This implies that you may need to use a larger wire size but you can not use a smaller one.
NEC 250.66 Has the table for sizing Grounding Electrode conductors. Exception B notes that where the portion of the GEC is connected to a UFER that portion of the conductor that is the sole connection to the UFER shall not be required to be larger than #4 AWG copper.
There are hundreds of examples showing a 200A service with water pipes, ground rods etc as the “Grounding Electrode system”. However, in modern practice we rarely ever have more than the UFER ground on a site as the electrode. However, there are wildly different theories and requirements on what size UFER ground is required. We have local jurisdictions require 1/0 for a 400A service while others require #2. We have seen plans from engineers specify 3/0 for a 1200A service and a few specify 500MCM for a 2000A service.
My understanding is when using a UFER ground you need 20’ of #4 Copper or 1/2” Rebar minimum in the concrete and are not required to have larger than #4 AWG copper between the electrode and the main service no matter what the service size is. Please correct me if I am wrong.
My questions:
Since 250.52 states “not smaller than” are there times where a concrete encased electrode would be required to be larger than #4? If so what would they be?
If the concrete encased electrode is the only electrode in the system does this require that the Grounding equipment conductor be sized per table 250.66 or that the portion between the electrode (UFER) and the service equipment be sized per the table?
NEC 250.52 States that you can use a Piece of rebar 20’ or more and minimum of ½” diameter or 20’ of “bare copper conductor not smaller than 4 AWG” as the “Electrode”. This implies that you may need to use a larger wire size but you can not use a smaller one.
NEC 250.66 Has the table for sizing Grounding Electrode conductors. Exception B notes that where the portion of the GEC is connected to a UFER that portion of the conductor that is the sole connection to the UFER shall not be required to be larger than #4 AWG copper.
There are hundreds of examples showing a 200A service with water pipes, ground rods etc as the “Grounding Electrode system”. However, in modern practice we rarely ever have more than the UFER ground on a site as the electrode. However, there are wildly different theories and requirements on what size UFER ground is required. We have local jurisdictions require 1/0 for a 400A service while others require #2. We have seen plans from engineers specify 3/0 for a 1200A service and a few specify 500MCM for a 2000A service.
My understanding is when using a UFER ground you need 20’ of #4 Copper or 1/2” Rebar minimum in the concrete and are not required to have larger than #4 AWG copper between the electrode and the main service no matter what the service size is. Please correct me if I am wrong.
My questions:
Since 250.52 states “not smaller than” are there times where a concrete encased electrode would be required to be larger than #4? If so what would they be?
If the concrete encased electrode is the only electrode in the system does this require that the Grounding equipment conductor be sized per table 250.66 or that the portion between the electrode (UFER) and the service equipment be sized per the table?