Re: Ufer ground
Originally posted by don_resqcapt19
The only reason for this change was to require the use of the rebar in a footing as a grounding electrode for new construction. 250.52 tells us what an electrode is, it does not give us a choice on using it if it is present. The "or" in 250.53(A)(3) only tells us that there are two types of concrete encased electrodes. This has no effect on the requirement in 250.50 that says you must bond all electrodes that are present.
As outlined above in 250.50 it states that, All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present
I fail to see any mention of rebar at this point. All I see is the referral to (A)(3) if it is present it shall be bonded together.
When I look at (A)(3) I see the title of, Concrete-Encased Electrode.
As I read through this section I see that there are two types listed as you pointed out above.
I fail to see any where in (A)(3) where I am told that if the rebar is present it MUST be used. All is see is the description of the two types.
250.50 tells me that if (A)(3) (a concrete encased electrode) is present it shall be bonded to the electrode system. After reading both sections I still can not see where I am told that I must bond any rebar of any kind to the electrode system unless I do not have the #4 in the footing and rebar is present.
Please point out where you are finding the words that mandates the rebar must be bonded if present.
I have done a little research on this and here is what I have found.
5-115 Log #1559 NEC-P05 (250-50)
Submitter: Michael J. Johnston, Int?l Assn. of Electrical Inspectors
Comments from the panel
BRETT: This proposal should have been accepted. The concrete encased electrode is proven to be an effective grounding electrode. By deleting "if available" it more clearly states the intention of the section that all electrodes be utilized to form an effective grounding electrode system. Many jurisdictions now amend this section of the NEC by deleting these words. The jurisdiction where I live does require the concrete encased electrode and it does not create an enforcement problem. Changes made by the code committees with less substantiation each code cycle always create some enforcement problems until the installers know the requirements being enforced. This proposal should be accepted.
JOHNSTON: The word available as used in this section is creating inconsistencies in the field relative to which grounding electrodes are required to be used in electrical installations. The concrete encased grounding electrode is a proven effective electrode and is inherent to the construction of most buildings or structures and should be included in the grounding electrode system as such. The NEC style manual recommends not using the word "available" to avoid this very type of inconsistency in application and enforcement Code rules.
Notice how the words concrete encased electrode is mentioned and no where does any one point to mandating that the rebar must be used.