Re: Ufer ground
Originally posted by don_resqcapt19:
jw,
There are no choices in 250.52(A). That section only defines the types of electrodes. There are two different types of concrete encased electrodes. I find nothing in 250.50 that says that if you have both types of concrete encased electrodes, that you only have to use one of them. All that are "present" are required to be bonded. If both types are present, then both types must be used.
Don
I think that you are adding something to 250.50.
All grounding electrodes as described in 250.52(A)(1) through (A)(6) that are present
It clearly states that the ones that are outlined in (A)(1) through (A)(6). I see nothing here that would lead me to think anything different than if (A)(3) is present it must be bonded.
The question comes form the definition of (A)(3) and this is where we are disagreeing.
(3) Concrete-Encased Electrode. An electrode encased by at least 50 mm (2 in.) of concrete, located within and near the bottom of a concrete foundation or footing that is in direct contact with the earth, consisting of at least 6.0 m (20 ft) of one or more bare or zinc galvanized or other electrically conductive coated steel reinforcing bars or rods of not less than 13 mm (? in.) in diameter
, or consisting of at least 6.0 m (20 ft) of bare copper conductor not smaller than 4 AWG.
Again I have bolded the ?comma? and word ?or? for you to look at. In my endeavors to gain a BS in Electrical Engineering I have to take some English classes. The classes have taught me that a comma stops one thought and begins another. My dictionary defines the word OR as, ?Used to indicate the second of two alternatives, the first being preceded by either or whether: Your answer is either ingenious or wrong. I didn't know whether to laugh or cry.?
Now plain old English tells me that either one of the two items mentioned in 250.52 (A)(3) would fulfill the requirements of the concrete encased electrode and that just because both are present does not in any fashion indicate that both are required to be used.
250.50 only requires that if a concrete encased electrode is present that it is required to be bonded to the electrode system.