here in WA all new buildings are required to have one. i have this issue now with a detached garage w/o any rebar access. he failed my two ground rods and pointed me in the direction of a ground ring. i am waiting till tomorrow morning to see what lies ahead. the building was built before the requirement hit July 1, so i am hoping that lets me out.
i am also hoping somebody will read me 250.50 out of a 2014 book to tell me if it's still there, which said i don't have to use the rebar if any demolition is required. that would probably put me back into having a ground ring. there used to, i believe, be wording to the effect that a ground ring could be only 20 feet of wire in the ground, but now i think that language is gone that is, a ring goes all the way around a building!!! i will have to ask mr lead inspector around here wtf he wants me to do.
As of the July 1 Electrical WACs a ground ring is no longer required if a ufer is not used, you can use ground rods but the resistance must be independently tested and be less than 25 ohms