Re: uh oh, another SA question
I will try this just one time and pay close attention to the way that I state this. I will be using the 2005 code.
In 210.70 a lighting outlet is required.
210.70 Lighting Outlets Required
Lighting outlets shall be installed where specified in 210.70(A), (B), and (C).
(A) Dwelling Units In dwelling units, lighting outlets shall be installed in accordance with 210.70(A)(1), (A)(2), and (A)(3).
(1) Habitable Rooms At least one wall switch-controlled lighting outlet shall be installed in every habitable room and bathroom.
As it is clearly stated a lighting outlet MUST be installed but I can install a switched receptacle instead of the lighting outlet.
Exception No. 1: In other than kitchens and bathrooms, one or more receptacles controlled by a wall switch shall be permitted in lieu of lighting outlets.
This switched receptacle is now the required lighting outlet.
In 210.52 (B) two small appliance circuits are required to be installed in certain rooms to supply receptacles.
(B) Small Appliances.
(1) Receptacle Outlets Served. In the kitchen, pantry, breakfast room, dining room, or similar area of a dwelling unit, the two or more 20-ampere small-appliance branch circuits required by 210.11(C)(1) shall serve all wall and floor receptacle outlets covered by 210.52(A), all countertop outlets covered by 210.52(C), and receptacle outlets for refrigeration equipment.
Take notice which receptacle outlets that is required to be supplied by these two small appliance circuits.
Once these requirements has been fulfilled then the exception under 210.52 (B) (1) can be applied.
Exception No. 1: In addition to the required receptacles specified by 210.52, switched receptacles supplied from a general-purpose branch circuit as defined in 210.70(A)(1), Exception No. 1, shall be permitted.
No where in 210.52 (B) is the lighting outlet required to be installed, therefore the exception to 210.52 (B) has nothing at all to do with the required lighting outlet. This exception allows the installation of more than the required small appliance receptacles as long as they are on the general purpose circuit. This inclusion of general purpose receptacles is for the use of light fixtures weather under, over or in the cabinets as well as hood fans as outlined in 422.16 (B) (4).
Take a few minutes and read 210.11 which mandate the required circuits for a dwelling unit and this will all fall in place with out confusion. Try as hard as you can to leave out what you think should be done and read what is written. This is so easy to understand that I find it hard to believe that people are having such a hard time with it.
As Scott has stated, this is plain black and white as long as the exception to .52 is left there and the exception to .70 is left there.
The one I like best is the under cabinet task fixtures that are hard wired but comes with a single receptacle mounted in them. I have never heard a word said about this 15 amp receptacle.