Originally posted by georgestolz:
Then what is your explanation for (C)(3)?
Well I see no problem with installing a three or four gain box with one duplex on the 20 amp small appliance branch circuit and the other two or three duplexes being on one or more 15 amp general purpose circuit.(3) Peninsular Counter Spaces. At least one receptacle outlet shall be installed at each peninsular counter space with a long dimension of 600 mm (24 in.) or greater and a short dimension of 300 mm (12 in.) or greater. A peninsular countertop is measured from the connecting edge.
Originally posted by georgestolz:
See what I get for not opening the book?
How about (B)(3), Mike? What say ye?![]()
Wouldn't this statement be moot, if any other circuits could supply receptacles on the countertop? "Three" is logically compliant with "not fewer than two."Additional small-appliance branch circuits shall be permitted to supply receptacle outlets in the kitchen and other rooms specified in 210.52(B)(1).
I am back...again. This time I actually read the article thoroughly. I offer this. I see nothing definitive that that?permits you to install general purpose (15 amp) circuits and receptacles in kitchen and dining wall space areas. I see nothing that says you can't either. I think the intent is to have all the receptacles fed from 20 amp small appliance circuits. But of course we know that intent is not the issue here. However as for the counter use receptacles I find clear evidence that you CAN NOT add general purpose (15 amp) circuits and receptacles after you have satisfied the minimum counter use receptacle spacing. 210.52 (B) (3) Receptacles installed in a kitchen to serve countertop surfaces shall be supplied by not fewer than two small appliance branch circuits........Originally posted by john m. caloggero:
Gentlemen: Siting in on the code panel as NFPA staff liaison and listening to the discussion, I offer the following answer. Once you have satisfied the 6ft wall space and countertop requirements with 2 or more 20A small appliance branch circuits, you can add additional receptacles on a 15A branch circuit for receptacle outlets that you may want to use for floor, table lamps, computer etc. where you may want to also switch them.
Scott, follow my reasoning on this:Originally posted by electricmanscott:
I don't care how you twist it around. "Receptacles installed in a kitchen to serve countertop surfaces shall be supplied by not fewer than two small appliance branch circuits." Crystal clear. You install receptacles to serve kitchen countertop they shall be supplied by at least two sa circuits. It does not say receptacles installed to meet spacing requirements shall be suppllied..... It says receptacles, period. If they serve the countetop they shall be sa circuits.
Which time? I've changed my mind a couple of times. One of the perils of an open mind is I'm easily persuaded.George, I thought you had changed your mind on this one.
As we look at (B)(1), the first thing we see is a list of the rooms that are affected by (B). Then comes the term "covered by". So, let's look at how this can be interpreted.But now this is where I thought you had changed your mind on: the wording used in (B) is 'covered by' and not 'required by'.
That's the kicker--the outlets covered by (A) are 6' & 12' receptacles installed to meet the wall space code. Anything beyond that may be a general purpose receptacle, but it is easily arguable that the receptacle was not installed to comply with 210.52(A), it was merely whimsy.210.52 does state that outlets that ANY outlet installed in a fashion that is 'covered by' (A)and(C), then it does tell us what to do with them.
The most critical crucial important monumentous stupendous problem with your (and my former) argument is it is not forbidden.It doesn't say we could sprinkle gp outlets in between the required ones.
I think I'll write a proposal for both schools of thought, maybe they'll accept one...Originally posted by georgestolz:
1. It doesn't work to interpret this as "each receptacle installed in a kitchen shall be supplied by two SA circuits." The breaker would trip.![]()
So that means we must consider the group as a whole. Okay, so now the group has to be supplied by not fewer than two SABC's. Once you have done this, you could have receptacles sprinkled in there that are fed from non-SABC's.
One issue I take with your portrayal of this exception is that you make it out to be expressly permitting GPBC-fed receptacles for any use, which is not what it says. If it meant "any use", it would say "any use". That exception specifically refers to the exception of 210.70(A)(1), for a specific use.Originally posted by jwelectric:
I also see that ?as specified in 210.52(B)(1)? also has an exception that allows the installation of general purpose receptacles.
'Cause what you say is what you say
Say what you say how you say it whenever you're sayin' it
Just remember how you said it when you were sprayin' it
So who you playin' with, huh?
-Eminem
Why?Originally posted by georgestolz:
[qb] One issue I take with your portrayal of this exception is that you make it out to be expressly permitting GPBC-fed receptacles for any use, which is not what it says. If it meant "any use", it would say "any use". That exception specifically refers to the exception of 210.70(A)(1), for a specific use.