Re: unbalanced load calc for 3 phase delta system
Vline = 120Vx1.732 = 208V
For a delta config,
Eline = Ephase = 240V in this case.
Vectors--or phasors depending on your age--are not for the faint of heart. That is the reason we have formulas which work quite well when when properly applied.
Rick, your formula applies to a wye configuration. For example, in a 120V/208V wye,Originally posted by RUWired:
rattus,E-L=E-Px1.732
Line voltage =Phase voltage x 1.732
Rick
Vline = 120Vx1.732 = 208V
For a delta config,
Eline = Ephase = 240V in this case.
Vectors--or phasors depending on your age--are not for the faint of heart. That is the reason we have formulas which work quite well when when properly applied.