unbalanced load calc for 3 phase delta system
Re: unbalanced load calc for 3 phase delta system
I have got a small doubt in this regards, In a delta wired 120/240 system , whether all phases would be center-tapped (or) any one of three phase would be center tapped ?.
As far my knowledge, any one of three phase would be center-tapped to get 120V supply.Whether Phase A (or) B(or) C.So this case , the number of single phase load will be connected / loaded with the same phase.
See here :
If phase A is center-tapped, It would draw the three phase load of 80Kva as well as single phase load of (34+41) Kva.So Phase A will be loaded with 80+(41-34) = 87 Kw
Other phases will take care of only 80 Kva load.
could someone clarify me ?
Jeyakumar
Kal-
What are you referring to as a phase? In a delta system it is easier for me to think of phase A-B, A-C, and B-C. In a wye system I think of phase A, B, and C. Does that help you?
Phase A-B is transmitting 80 kVA, phase B-C is transmitting 80 kVA, and phase A-C is transmitting 121 kVA. The neutral of the center tapped A-C phase will transmit (41 kVA -34 kVA) = 7 kVA.
Therefore the answer to the original question (Rattus' second post):
Ia = 835 A
Ib = 890 A
Ic = 577 A
I left the relative angles out.
[ February 11, 2006, 09:49 AM: Message edited by: Zifkwong ]
Jeyakumar,
You would center tap only one transformer because the CT is also the grounded neutral for the 120/240V loads.
In this case, winding A-C is center tapped and it provides 80KVA + 34KVA + 41KVA = 155KVA. You add these powers, not subtract.
zifkwong got the correct answers first; then I went back and corrected my error. However, I think Ib should be 577A if we center tap winding AC. Zif's numbers are correct though. Go back and review these posts for the correct numbers.
[ February 11, 2006, 09:52 AM: Message edited by: rattus ]
Originally posted by RUWired:
rattus, i finally see where our differences are.When someone says to me they have a "connected" load of 80 kva a-b-c,i think they are saying its 80 between a and b, 80 between b and c, 80 between c and a.Your saying each line to the coil is 80kva making a-b 240kva and so on. now making it a "connected" load of 240 kva.(and then doing the math from there).
Rick
The original post stated 80KVA per phase. That says it all. Now you need to convince yourself that,
Ib = 333Ax2cos(30) = 333Ax1.732 = 577A
The reason that 30 degrees appears instead of 120 degrees is that we must take the difference of the two phase currents rather than the sum--Kirchoff's Law.
Calculation of Ia and Ic is a bit more difficult.
Edited to correct DA mistake.
[ February 11, 2006, 12:33 PM: Message edited by: rattus ]
I could interpret that to mean 80 kva total or as you say, 80 kva between phases. I would have to ask for a clarification of the statement.
To me the phrase "line to coil" is confusing. Each secondary coil has 80 kva of load making the load connected line to line (ab,ac,bc).
I saw a lot of calc's but i did not see any one say anything about this being a high leg. If you center tap B and C on a Delta on 3 phase 3 wire system to get 120/240, your voltage on A to ground is 277V?
No, it is 208 volts.
Don
I have to say once again,The best thing about our trade is seldom does a day go by with out learning something new, seeing something in a different light, or understanding different concepts.
Rick