underground serviced meter base distance from windows

Status
Not open for further replies.
Regarding the NEC I would say no, the 3' distance is typically for overhead conductors where the service conductors, drop and service point are exposed. The POCO may have separate rules but I doubt that most will care how close the meter enclosure is to the window.
 
The 3' rule definitely does not include the meter base. I had an inspector fail me for this about 20+ years ago. I asked him to go back to the office and ask the more experienced inspectors. He later called and said everything was fine. The 3' is for the dip loop etc for overhead services
 
The 3' rule, I believe, is a POCO rule and is for overhead services. The intent is To prevent someone from "opening" a window and having the ability to grab the conductors or touch the splice point. Obviously it is only for cases where windows open.
 
I can't post the section but the 3' rule is in the NEC it only applies to open conductors, not cables, conduits or enclosures.
 
I can't post the section but the 3' rule is in the NEC it only applies to open conductors, not cables, conduits or enclosures.

This what you want?

230.9 Clearances on Buildings. Service conductors and
final spans shall comply with 230.9(A), (B), and (C).

(A) Clearances. Service conductors installed as open conductors
or multiconductor cable without an overall outer
jacket shall have a clearance of not less than 900 mm (3 ft)
from windows that are designed to be opened, doors,
porches, balconies, ladders, stairs, fire escapes, or similar
locations.

Exception: Conductors run above the top level of a window
shall be permitted to be less than the 900-mm (3-ft)
requirement.

(B) Vertical Clearance. The vertical clearance of final spans
above, or within 900 mm (3 ft) measured horizontally of,
platforms, projections, or surfaces from which they might be
reached shall be maintained in accordance with 230.24(B).

(C) Building Openings. Overhead service conductors
shall not be installed beneath openings through which materials
may be moved, such as openings in farm and commercial
buildings, and shall not be installed where they
obstruct entrance to these building openings.
 
Cigars are bad for your lungs anyway
Thank you. I know that rule pertained to overhead serviced meters, etc., but when I read the underground meter requirements on my POCO website, it said the meter is "recommended to be 3 feet from windows and doors". I wanted to get your opinions. I did call Duke E today and they told me I am ok to mount it closer than 3 feet to window
 