I don't agree with that statement. There are code "experts" on both sides of that issue. I agree with those experts who say that NM and UF cannot be installed in complete raceway systems.If you are commenting on the NEC's allowance of UF in conduit, it has been generally agreed that it is not the intent of the code to restrict the use of UF or NM cable from being installed in a raceway
DonCables shall be permitted to be installed where such use is permitted by the respective cable articles.
Bryan I agree with your statement, and so does the NFPA, which is why the amendment was being considered. From my understanding, the reason it is not going to be in the 2005 is that the CMP simply ran out of time. By the way, it is also my understanding the cable wiring methods were supposed to be permitted for this use, but the 2 CMP's for cables and raceways simply didn't communicate well enough between them.Originally posted by bphgravity:
The scope of the NEC is in no way violated by the use of these cabling systems in this method.
Edited to address my incoherent babblingOriginally posted by ryan_618:
Hi Bennie. The debate is this: 352.22 Says that cables may be installed in the raceway (RNC in this case) when the it is permmited by the cable article. The NM cable article (334) makes no such allowance.
So, while I agree with Bryan in that it was an error, I happen to agree with Don's perspective more, because that is what the code says, like it or not. As I noted on one of my posts, the CMP responsible for the mistake has acknowledged to me (perhaps off the record) that it was a mistake, but that doesn't change the wording of the code.