The 100A ckt. was someone else’s idea, I would never have done that unless ordered to in writing.
I knew that
I was saying either the #1 or 1/0 is better than the 100
The 100A ckt. was someone else’s idea, I would never have done that unless ordered to in writing.
I knew that
I was saying either the #1 or 1/0 is better than the 100
All we got from OP was picture of nameplate and very limited information, I'd at looking at what this machine truly is and taking that information into consideration before just assuming a 100 amp circuit will be fine. But from the information we do have seems there is a good chance 100 amp circuit would seldom if ever be overloaded.I run across this kind of thing now and then. I would probably put a 150A MCCB on it and have the electrician run 1/0 copper. It is more cost effective than worrying about it and having to explain it to a bunch of people, and then having meetings about it. No one will argue that a 150A MCCB with 1/0 copper is not acceptable. The $50 or $100 you might save by using a smaller conductor is not worth the aggravation of having to explain it later.
JMNSHO
Is a 20 HP motor plus controls all there is for loads? If so and even if on VFD driven a 60 or 70 amp breaker probably never trips because of the soft start nature of VFD driven applications.Thanks for all the replies. I don't have more information on the machine to offer right now. The 20 HP motor is VFD, 100 amp would likely work load wise, but to be on the safe side of legality I'll probably do #1 and 125A CB.
20 Hp plus small motors, don't have info on the small motors yet.Is a 20 HP motor plus controls all there is for loads? If so and even if on VFD driven a 60 or 70 amp breaker probably never trips because of the soft start nature of VFD driven applications.
20 HP @ 208 or 240 volts only requires #4 copper before any adjustments come into play, if that nameplate is 101 amps there must be other loads though.
Why not #2 copper? Maybe even 110 amp breaker?#1 copper, 125 amp breaker.
Why not #2 copper? Maybe even 110 amp breaker?
I agree with #2 but would still use the 125.
IMO, 35KVA = 91.85 3-phase amps
15 hp spindle largest motor = 42 amps x 1.25
91.85 + 10.5 = 101.5 amps abt nameplate.
In post 26 OP stated 20 hp motor plus other motors. The 101 amps is fla not mca.