I've measured the difference of parallel conductors that were trimmed by the POCO at the pole top. 5-10 amps. Just how much difference in length would be needed to create so much heat?
It would take a lot of difference in length to make any real difference assuming that the length is the only difference.
If you have a 2000 amp circuit using 5 sets of conductors and 4 of the sets are 50' and the last set is 55'.
The four 50' lengths would carry 407 amps and the 55' one would carry 370 amps. If I make the long on 60' it would carry 345 amps and the four 50' ones would carry 414 amps.
It really is based on the percentage difference in lengths, and there is much more impact where the run is short.
if I have the same 2000 amp circuit with five sets having the lengths of 20', 22', 24' 26' and 28' the currents would be 473, 430, 394, 364 and 338.
(note the numbers have been rounded so they will not total exactly 2000 amps)