Just looking for some other input on this situation- a customer failed a recent home inspection.She was cited for having ungrounded 3 prong receptacles serving her kitchen countertop. All of the rest of the receps in her home were the old two prong variety. All of the outlet boxes in the house are plastic and all of the wiring feeding them appears to be old cloth insulated type(no ground).In trying to fix the situation in the most unintrusive,cost-effective way, I suggested replacing the three prong receps with gfcis.The inspector will not accept this solution.He says if I install the gfcis, they still must be grounded.I have to do that or replace the three prong receps with the original two prong style(which should be gfcis anyway, since they are serving a kitchen countertop.)Any advice or suggestions?