Supplemental and some here think
Supplemental and some here think
Mike, Thanks for commenting on supplemental from my quote you made in post #99. Some here think I believe that a CEE is supplemental. Please read my post #50 where I asked the moderator if the CEE is supplemental. I was not the one who agreed with the return answer in #52 post. Someone here is reading between the lines.
Go back to #52 and give someone here more credit. THE CEE IS NOT SUPPLEMENTAL! Taking a partial quote from article [250.53(E)], it states "that portion of the bonding jumper that is the sole connector to the SUPPLEMENTAL grounding electrode shall not be required to be larger than #6 AWG copper wire or #4 AWG aluminum wire." The CEE in 2008 NEC parlance is non-supplemental as based upon most new construction starts requiring #4 rebar and #4 AWG conductor bonding. Check the rebar requirements in the UBC or IRC. (R403.1.3.1)
Bob, Reality is that a 100 AMP service using #8 AWG Cu to a CEE requires a protective raceway in conduit [250.64(B)] that is so expensive, labor intensive and ridiculous. Reason, when was the last time you saw new start-up residential home construction or multi-dwelling electrical service meter-Center installations using a 100 Amps.
Get real and refer back to some of your other threads suggesting #4 AWG conductors bonds to CEE's. I can understand why this thread is very confusing especially when I read your link to the State of Mass. references to CEE installations.
What is going on here? Have I offended you? If so, I did not intentionally. This whole thread is regurgitation of code being sliced into segmented statements. Is this all about my questioning your hypothetical comments? Sorry if I am confused. rbj
Supplemental and some here think
Mike, Thanks for commenting on supplemental from my quote you made in post #99. Some here think I believe that a CEE is supplemental. Please read my post #50 where I asked the moderator if the CEE is supplemental. I was not the one who agreed with the return answer in #52 post. Someone here is reading between the lines.
Go back to #52 and give someone here more credit. THE CEE IS NOT SUPPLEMENTAL! Taking a partial quote from article [250.53(E)], it states "that portion of the bonding jumper that is the sole connector to the SUPPLEMENTAL grounding electrode shall not be required to be larger than #6 AWG copper wire or #4 AWG aluminum wire." The CEE in 2008 NEC parlance is non-supplemental as based upon most new construction starts requiring #4 rebar and #4 AWG conductor bonding. Check the rebar requirements in the UBC or IRC. (R403.1.3.1)
Bob, Reality is that a 100 AMP service using #8 AWG Cu to a CEE requires a protective raceway in conduit [250.64(B)] that is so expensive, labor intensive and ridiculous. Reason, when was the last time you saw new start-up residential home construction or multi-dwelling electrical service meter-Center installations using a 100 Amps.
Get real and refer back to some of your other threads suggesting #4 AWG conductors bonds to CEE's. I can understand why this thread is very confusing especially when I read your link to the State of Mass. references to CEE installations.
What is going on here? Have I offended you? If so, I did not intentionally. This whole thread is regurgitation of code being sliced into segmented statements. Is this all about my questioning your hypothetical comments? Sorry if I am confused. rbj