Wow! Yeah I heard about that before. I don't understand why he would tackle a guy from the team he's a fan of. Must be a mental disturbance that affects Patsies fans.I may be a wise guy but I am not an idiot.
Contractors tend to get tripped up using a smaller conductor other than a #4 AWG when the CEE is installed and inspected prior to the foundation close-in . The AHJ inspector wants to see a #4 AWG. Reason? Without evidence of any H2O and steel structure the AHJ require UFER sign-off with the #4 AWG GEC. (maximum [250.66] conductor compliance regardless of service size.) Call it CYA if you like.
That's fine if you feel that someone should inspect a CEE that way, but it doesn't change the fact that it goes outside of the requirements of the NEC. So call it a local requirement or just the way things are done in a particular place but don't call it an NEC requirement because it isn't and it may be misleading to someone to say that it is.
I agree on that providing a metal H2O pipe gets installed, otherwise, requiring the GEC to be coming from the UFER 2008 installation is an NEC 250.50 basic requirement.
In 2008 reality, a new start-up residential or commercial electrical project must begin with installing the CEE per [(250.52(A)(3)]
So laugh at me or throw eggs, I am giving a reason from experience why the Illustration must be changed for 2008 configurations.
I agree on that providing a metal H2O pipe gets installed, otherwise, requiring the GEC to be coming from the UFER 2008 installation is an NEC 250.50 basic requirement.
For me personally, I always had it in my head I think from 4th year of school that there were such a thing as a suplemental electrode, for example in a home the copper water line entering from the ground being the primary and then driving 1 ground rod and it being the supplemental.I have read this very long thread and have some questions.
Many times throughout this thread there have been many references to ?Supplemental Electrodes? even calling those electrodes outlined in 250.52(A)(4) through (A)(8) supplemental electrodes.
I have always thought that any and all electrodes outlined in 250.52 were to be bonded together to make ONE big electrode, is this not true?
Are not all these electrodes that are bonded together one big electrode?
If they do constitute one big electrode then there is not any supplementation but only one electrode system or one giant electrode.
I have also always thought of what everyone calls ?Supplemental Electrodes? to be those outlined in 250.54 which are actually auxiliary grounding electrodes.
I have always thought that the Grounding Electrode Conductor had to originate in the service equipment and any conductor that tied (bonded) any two or more electrodes together to make one large electrode was a bonding jumper. An example of this would be that conductor from rod one to rod two is a bonding jumper not a grounding electrode conductor. Again is this true?
You all have me so confused that I am beginning to wonder if the driven conduits are worth my time to drive them.
Many times throughout this thread there have been many references to “Supplemental Electrodes” even calling those electrodes outlined in 250.52(A)(4) through (A)(8) supplemental electrodes.
I have also always thought of what everyone calls “Supplemental Electrodes” to be those outlined in 250.54 which are actually auxiliary grounding electrodes.
I have always thought that the Grounding Electrode Conductor had to originate in the service equipment and any conductor that tied (bonded) any two or more electrodes together to make one large electrode was a bonding jumper. An example of this would be that conductor from rod one to rod two is a bonding jumper not a grounding electrode conductor. Again is this true?
Yes I agree that 250.53(D)(2) uses the word ?supplemented? but once this requirement is fulfilled then does not this constitute one electrode system or in other words one electrode.Only the water pipe is required to be supplemented by another electrode.Many times throughout this thread there have been many references to ?Supplemental Electrodes? even calling those electrodes outlined in 250.52(A)(4) through (A)(8) supplemental electrodes.
So then this means that the illustrations outlined in this thread are a compliant installation as each illustration only has one ground electrode conductor, is this correct?Yes the GEC originates at the neutral, other conductors used to connect the electrodes together are bonding jumpers.
Then would it be safe to say that once a ?Supplemental Electrode? has been installed and bonded back to all the other electrodes outlined in 250.52 that there is only one giant electrode system and the words ?Supplemental Electrodes? can be forgot about?Auxiliary electrodes and supplemental electrodes are two different things.
grdrod said:In 2008 reality, a new start-up residential or commercial electrical project must begin with installing the CEE per [(250.52(A)(3)] and be inspected prior to concrete close-in. In the process the CEE precedes any structure or water piping installations until the foundation is poured.
grdrod said:Contractors tend to get tripped up using a smaller conductor other than a #4 AWG when the CEE is installed and inspected prior to the foundation close-in . The AHJ inspector wants to see a #4 AWG. Reason? Without evidence of any H2O and steel structure the AHJ require UFER sign-off with the #4 AWG GEC. (maximum [250.66] conductor compliance regardless of service size.) Call it CYA if you like.
There is no NEC requirement to use a 4 AWG GEC to a CEE unless the service size and 250.66 requires it.
I agree, but if wire is installed AS the CEE, then #4 AWG is required as a minimum (250.52(A)(3))
Without a doubt that is true, and I have not said otherwise. If I make a CEE of wire I have to use at least 4 AWG but the GEC or bonding jumper connecting it to the panel or GES could still smaller then 4 AWG.
I agree, It was a "supplemental" post
Thank you for the compliment. Because of the post below he should look at the grounding electrode system as being one giant electrode then he will have a better understanding of the idea of grounding.Mike you are very bad at playing dumb. I personally don't really see why your so concerned about this supplemental junk when we still have not gotten by these problems.
These are not supplemental electrodes but they are just plain old electrodes that can stand alone if no other electrode is present.Roger, If there is no metal underground water pipe, then the CEE is not supplemental. In fact the first three electrodes mentioned in [250.52] are excluded from the [250.50] last sentence...."Where none of the grounding electrodes exist, one or more of the electrodes specified in 250.52(A)(4) through (A)(8) shall be installed and used." These are the supplemental electrodes used in lieu of the common electrodes not present. The 250.52(A)(1) is becoming extinct in residential (and commercial high-rise) opting for PEX or CPVC. This is the main reason for specifying CEE with any structure. rbj
All of this can very confusing if one lets a lot of needless information enter the equation. I think that this is the problem with some of the people posting in this thread. The simple way of looking at the electrodes is to simply look at all the items outlined in 250.52 as comprising one electrode and then installing the grounding electrode conductor to the electrode.It seems there are several issues at play here: 1) The installation of a CEE and its proper use, conductor size, and connection 2) When are we required to use irreversible or cadweld type connections 3) And now the topic of "supplemental" electrodes has come up Can you say "confusing?"
he should look at the grounding electrode system as being one giant electrode then he will have a better understanding of the idea of grounding.
These are not supplemental electrodes but they are just plain old electrodes that can stand alone if no other electrode is present
The simple way of looking at the electrodes is to simply look at all the items outlined in 250.52 as comprising one electrode and then installing the grounding electrode conductor to the electrode.
We address a metal water pipe from Table 250.66 and every other item outlined in 250.52 can be addressed in the same manner.
some here think that every conductor installed on the electrode system is part of the grounding electrode conductor
When someone is sold on this idea it can be very difficult to change their mind. ..