Here is another illustration from the 2008 NECH.
Another from an earlier handbook.
This second one points out the difference between a GEC and a bonding jumper. :smile:
Here is another illustration from the 2008 NECH.
#3 The UFER (CEE) must be a continuous GEC with no splices from the Main Disconnect panel terminal bar
#(Service grounded and Equipment grounding). This requirement is very subtle in that the water pipe electrode can be a continuous #6 [250.52(A)(1)]
#while the UFER must have a continuous #4 GEC [250.52(A)(3)] in order to be compliant to [250.58] Common GEC's and [250.64(C)] Continuous GEC's.
I must admit it is one of the myths that I beleived. For example in homes whenever I've driven 2 ground rods I've always thought that they had to be continuous. Something I've just realized is the following: In the past, there have been homes that we've wired (standard 200amp service, 4/O AL which should require the GEC to be #2 AL or #4 CU), that didn't have a metal underground water pipe, so in that case we always have just driven 2 ground rods with #6 CU and that's it. So technically in this case that was wrong, because nowhere did we install the properly sized GEC (#2 AL).That is one of the most persistent myths in the electrical trade, and there is still widespread ignorance about how the GES conductors are to be connected. Thankfully both of those graphics clear up the confusion quite well.
In the past, there have been homes that we've wired (standard 200amp service, 4/O AL which should require the GEC to be #2 AL or #4 CU), that didn't have a metal underground water pipe, so in that case we always have just driven 2 ground rods with #6 CU and that's it. So technically in this case that was wrong, because nowhere did we install the properly sized GEC (#2 AL).
Something I've just realized is the following: In the past, there have been homes that we've wired (standard 200amp service, 4/O AL which should require the GEC to be #2 AL or #4 CU), that didn't have a metal underground water pipe, so in that case we always have just driven 2 ground rods with #6 CU and that's it. So technically in this case that was wrong, because nowhere did we install the properly sized GEC (#2 AL).
right but in that case what was my GEC? My GEC is suppossed to be a #2 AL or #4 CUActually it was right, because in that case nothing larger than #6 is required. A ground rod never needs a GEC larger than #6 regardless of the service entrance conductor size.
Yes but where was my GEC? Doesn't there need to be a #2CU or #4 AL sized per 250.66 for the GEC (to something, not necessarily the ground rod) since I had a 4/O AL service entrance conductor?That wasn't wrong at all. No matter what size the service is, the sole connection to ground rods is never required to be larger than #6, nor does it need to be.
right but in that case what was my GEC
Actually doing it continuous will save the expense of one connector.I must admit it is one of the myths that I beleived. For example in homes whenever I've driven 2 ground rods I've always thought that they had to be continuous.
No, the connection to the rod(s) only had to be #6 CU so you were correctso in that case we always have just driven 2 ground rods with #6 CU and that's it. So technically in this case that was wrong, because nowhere did we install the properly sized GEC (#2 AL).
I guess when using 2 ground rods one for the primary and the other for the secondary we should've used a #4 CU GEC to the first rod and then we could've used #6 CU to the second rod.
Yes but where was my GEC? Doesn't there need to be a #2CU or #4 AL sized per 250.66 for the GEC (to something, not necessarily the ground rod) since I had a 4/O AL service entrance conductor?
Remember the purpose of the GEC is for lightning protection and accidental contact with high voltages.
I was thinking that somewhere I had to have a primary GEC sized per 250.66, b ut since nothing was available except for 2 rods then #6 CU to the rods covers it.
So let's say lightning strikes the home wouldn't most of the current from the lightning travel back to the POCO transformer via the neutral vs. going right into the ground via the ground rods?
So let's say lightning strikes the home wouldn't most of the current from the lightning travel back to the POCO transformer via the neutral vs. going right into the ground via the ground rods?
So in my example before where the water pipe was plastic and the only GEC is my #6 CU to the rods, would just 1 rod be sufficient or do I need 2?What helps is to remember that there really is no such thing as a "primary GEC." As the illustrations show there are multiple GEC's to consider, particularly in an industrial or commercial establishment
So in my example before where the water pipe was plastic and the only GEC is my #6 CU to the rods, would just 1 rod be sufficient or do I need 2?
Got it thanks....If you can show that the rod is 25 ohms or less one is sufficient, but even if you own the test equipment it is usually cheaper to just drive two rods and go home.
Roger
Okay. I got it now. This has been a good refresher for me. I was thinking that somewhere I had to have a primary GEC sized per 250.66, b ut since nothing was available except for 2 rods then #6 CU to the rods covers it. Thanks for clearing that up guys.
Same thing holds true for the CEE. #4 Cu is the largest GEC required to the CEE even if table 250.66 calls for a larger conductor.