- Location
- Massachusetts
but the detail is still incorrect. Please refer to [250.52(A)(3)] and the CEE minimum conductor is not smaller than a #4 AWG x 20ft. conductor.
The images are correct.
There is no requirement that 4 AWG be run continuously from the footing to the panel.
With a typical 100 amp service I could run just 8 AWG copper GEC from the panel to the 20' of rebar or 4 AWG located in the footing.
The only requirement with 4 AWG is if you choose to create a concrete encased electrode out of 'wire' that it will be at least 20' of 4 AWG encased in concrete.