himooo said:I want all data available for UPS systrms
brian john said:Send me a list of questions and I will answer anything you care to know and send you pics (weak drawing I completed).
himooo said:1- what types of UPS and how to chooose
2- how it will connected to the generator and it needs isolation transformer or not (because of the harmonics)
3- what will happen in case of power failure
dereckbc said:3. Huh? Well we hope the loads on the UPS keep right on ticking and never know the site lost power. Further we hope the generator starts up and takes place of utility power before the batteries in the UPS discharge and the "ON" light goes out on the equipment and everything gets real quite. :smile:
Well I don't pretend to know what a gas plant would need to shutdown, but the design process is th esame for any UPS, you need to know what the size of the load is and how long you need to supply that load with batteries. Since the question is generic I can only give genric answers.RHJohnson said:OP refer's to Gas Plant......UPS would only be sized to bring about an orderly and controlled and safe shutdown. Not operate the plant until power restored.