Bob and Brother, I understand what you are saying. And in the case of long wires with VD issues, I can see some value in increasing the EGC. But let me point out that you could have used #12 wire and a #12 EGC for that 1000 foot run, and not have violated any code article (and depending on what the load was, it is not impossible that the voltage at the end of the run would be enough for proper operation). From that I infer that the amount of fault current that would be available, noting that the current would flow through the impedance of two very long #12 wires, would still be enough to trip the breaker. I base that claim on the fact that we are allowed to make that installation. So when you increase the size of phase conductor (and, irrelevantly, the neutral as well), you are into my scenario #2. The scenario #1 trip was fast enough, or it would not have been allowed. #2 is faster still. So why are we forced to make it faster than scenario #2? :?