But the 2020 NEC also added:Section 250.122 has changed about teason but the latest version makes it clear if you increase the ungrounded conductors for any reason, the egc is to be increased in size
250.122(B) said:Exception: Equipment grounding conductors shall be permitted lo be sized by a qualified person to provide an effective ground fault current path in accordance with 250.4(A)(5) or (B)(4).
First of all, in my view, only a licensed professional electrical engineer would be "qualified," in the sense intended by this exception. Secondly, as such a PE EE, I would never try to take advantage of this exception.So if you're qualified. . . .
The same definition whenever the term is used in the NEC, as found in Article 100:What's the NEC definition of a qualified person when applying 250.122(B)?
I will disagree, as there is an Article 100 definition to refer to. So there's no particular "sense" to this usage in 250.122(B) Exception, there's just the definition.First of all, in my view, only a licensed professional electrical engineer would be "qualified," in the sense intended by this exception.
This article changed at least twice over the past several cycles (for which I am grateful). The 2023 edition makes it clear that choosing a "different" (at this point, I won't use the word "increase") size conductor because you have a high ambient temperature or you have many current-carrying conductors in the same conduit does NOT constitute an "increase in size" (OK, I used that word this time) and does not require a larger EGC.. . . the latest version makes it clear if you increase the ungrounded conductors for any reason, the egc is to be increased in size
The only definitive starting point is 'code minimum.'I tried to make the point that the phrase, "increased in size" makes no sense whatsoever, if you don't clarify the starting point "i.e., increasedfrom what."
True.The only definitive starting point is 'code minimum.'
My response would be:If I am performing a design review of the proposed installation, I will insist on seeing the associated calculation.
For the situation where case 1 above doesn't hold, that minimum sized ungrounded conductors would have unreasonable voltage drop, and hence there is reason to be concerned about excessive ground fault impedance.Ask yourself this: if I can use #10 ungrounded conductors in a 20 amp circuit and stick with a #12 EGC, why eas the "upsiae the EGC rule" ever included in the NEC?
In this instance, the "equipment" consists of wires, conduit, the voltage source and its internal impedance, and inductive loads (e.g., motors) installed in the facility. Wires have resistive and inductive reactance, the later of which depends in part on the material and size of the conduit, and both of which depend on the point along the wire that the fault takes place.Qualified Person. One who has skills and knowledge related to the construction and operation of the electrical equipment. . . .
What if someone decides later to utilize that larger conductor at its full capacity?2) I choose to then upsize the ungrounded conductors. Maybe because I think 1% VD will save me money in the long run, maybe because I have a lot of one size on my truck, or maybe because I like numbers to be multiples of 4. Regardless, the ground fault impedance has simply decreased slightly from case 1 above, and so my EGC is still an "effective ground fault current path" without upsizing the EGC.
Sure, but that's a future problem on them, to check that the EGC size is adequtae.What if someone decides later to utilize that larger conductor at its full capacity?
Could that possibly render the original EGC size too small now?
Sorry, Wayne, but that reasoning is not valid. The phenomenon of voltage being dropped along a wire carrying normal load current, a situation in which the EGC is not a player, is nothing like that of extremely high current under fault conditions, for which the job of the EGC is to ensure that the OCPD is able to quickly clear the fault.My response would be:
1) Here's the VD calculation using the . . . .
Charlie, you obviously know a lot about the details of that calculation. So please tell me this: If for a certain set of circumstances, ungrounded conductor size X and EGC size Y calcs out to be OK, and then the only change I make is to increase the ungrounded conductor size, does it automatically still calc out to be OK? I'm under the impression that it does.You might just need a larger EGC to overcome this situation. Or you might not. How does one tell the difference? By performing a calculation. That is where the PE EE comes into the process.
I will concede that this is the one thing that always confused me. It made me wonder why 250.122(B) was ever put into the code. Changing from #12 to #10 phase conductors will reduce the overall circuit impedance, increase the available fault current, and cause the OCPD to respond more rapidly. Why then, do we need to reduce the fault circuit impedance even further by using a #10 EGC?2) I choose to then upsize the ungrounded conductors.. . the ground fault impedance has simply decreased slightly from case 1 above, and so my EGC is still an "effective ground fault current path" without upsizing the EGC.