Strathead, I welcome all opinions and cherish everyone's right to disagree. I also honor and respect the knowledge and experience it takes a person to become a Journeyman or Master Electrician. I would never question such a person's qualifications to design and install electrical equipment. But those qualifications are not the same as would be needed to ascertain that an effective ground fault return path exists even if you don't upsize the EGC. See my post #14 for my reasoning.
The science of logical reasoning (OK, I recall this from a college course I took 50 years ago) includes several "classical" invalid arguments. One goes something like this:
Person 1 - "What needs to be done here is XXX."
Person 2 - "Can you prove that?"
Person 1 - "This is my area of expertise. I am fully qualified to make this call. Trust me."
It may turn out that Person 1 is right. But the proof totally failed to prove anything. This type of invalid reasoning is called, "begging the question." This is what comes to my mind when I read statements along the lines of, "I am qualified enough to know I don't have to upsize my ground." How would a reviewer know who made the call not to upsize? How would a reviewer know that person's qualifications? A PE has the privilege (and indeed the duty) to declare to the world (by sealing and signing design documents) that, "This work was done by me or under my supervision." Is that needed, in order to take advantage of the exception under discussion here? I think so. You and others have disagreed.
Bottom line: If I am performing a plan review, or perhaps an on-site inspection of an installation in progress, and I see a 20 amp circuit with #10 phase and neutral conductors and a #12 EGC, and if there is no written justification for not using a #10 EGC, then I will cite this as a code violation.