I was pointing out a GFCI that likely is in the list, again I did not look at the list.I think it would not need to be treated any differently than any other circuit breaker.
I was pointing out a GFCI that likely is in the list, again I did not look at the list.I think it would not need to be treated any differently than any other circuit breaker.
I believe you meant to say "blank face GFCI".
Do you have any further code references to substantiate your opinion other than "let me just say....". Now, please understand, I strongly lean toward agreeing with you, but I have always used the code to reinforce my stand on things (legality and all that), and there just seems to be so much gray area on this.
. . . would it still qualify as a switch?
So, using UL's White Book wording to just ever so slightly say it another way, GFCIs "with 'ON' and 'OFF' markings . . . are . . . intended to be used as 'ON/OFF' controls of . . . loads". To me, the on/off control of a load is the very definition of a "switch".GROUND-FAULT CIRCUIT INTERRUPTERS (KCXS)The ??TEST?? and ??RESET?? buttons on the GFCIs are only intended to check for the proper functioning of the GFCI. They are not intended to be used as ??ON/OFF?? controls of motors or other loads unless the buttons are specifically marked ??ON?? and ??OFF.?? Products with ??ON?? and ??OFF?? markings have been additionally Listed under Motor Controllers, Mechanically-operated and Solid-state (NMFT).
I agree with that, thanks for digging that up.To me, the on/off control of a load is the very definition of a "switch".
Ummm...they do have a 1.5 HP rating but that has nothing to do with it being a disconnection means.P&S dead front GFCIs are listed as disconects. I don't recall the wattage, but 1.5 hp comes to mind.
But I will note...they do have a distinct "on and off" button layout.
So it seems that in NMFT these BF GFCI's have been tested for use with 1.5 HP motors. Interesting.....I see that in UL Guide NMFT now.And a trip indicator light that comes ON when the power is disconnected from the output side.
Ummm...they do have a 1.5 HP rating but that has nothing to do with it being a disconnection means.....
So it seems that in NMFT these BF GFCI's have been tested for use with 1.5 HP motors. Interesting.....I see that in UL Guide NMFT now.
But still not convinced they qualify as a Disconnection means....just as a motor controller.
Would a single pole Decora switch be allowed as a disconnect in the same scenario?
Huh? So discos don't need to be labeled for their max. disconnecting ratings?
A good question, but I think the issue is that if not a dead front GFCI, some other kind of disconnect still needs to be provided. Admittedly a snap switch is cheaper, but the DF GFCI might be considered to have added value.I'm wondering why GFCI protection ii's being discussed to begin with? I believe the OP states 2005 NEC.
Yes, it has an on/off switch. Also, the P&S gfci's trip when first energized, but I'm not sure if they'll trip again if the power is interrupted, then restored.