Again, remembering that this point of Code is with respect to the 2005 NEC, I wonder if, as stated, your meaning is a little over broad. A blank face GFCI device with marked ON and OFF is described in the White Book as capable of controlling a common residential dishwasher. As for the disconnecting means, use the 2005 NEC 422.31(B) provision for locking an out-of-sight breaker or switch. While GFCI protection of the dishwasher is not required under the 2005 NEC, it is not prohibited.
So, I'd be inclined to say: the "ON/OFF" marked BF GFCI is listed to control the appliance, but cannot be operated to prevent re-energization if in the ON state upon power interruption, and, is therefore, not, all by itself, the disconnecting means of 2005 NEC 422 III.
The reason I make this distinction at all is because, down the road in the 2014 NEC, both AFCI and GFCI will be required for this common residential dishwasher.