So back to the OP's situation, what are the typical options for connecting to the primary of a transformer off at LRG system? I did ask if there was a neutral available and did not get an answer. Would a Delta Wye transformer be preferable in this situation?Just to be clear, MGN is different than LRG. If you have LRG, you don't have MGN, and vice versa. If you have LRG at source transformer, you typically don't (wouldn't ever?) bring out the neutral (direct from X0) with the phase conductors.
This snip kinda shows it. NGR = neutral grounding resistor