mivey
Senior Member
Doesn't have to because it does not apply but if it makes you happy you can use the easements clause.Please do tell where in NEC 90.2(B) it allows that
The NESC applies so the NEC can conflict or not but has no standing. Both have worked on wording to clear up any perceived conflicts, but I would agree they need more work.or anywhere in the NESC it contradicts NEC 90.2(B) on this issue?
They do not negate each other since they cover different installations. Perhaps the NESC wording will help you:And or negates specifically what it says in NEC 90.2(A)(4)
NESC 011, Scope.
A. Covered
1. Supply and communication facilities (including metering) and associated work practices employed by a public or private electric supply, communications, railway, trolley, street and area lighting, traffic signal (or other signal), irrigation district or other community owned utility, or a similar utility in the exercise of its function as a utility.
...
4. Street and area lights that provide a supply of lumens where these facilities are supplied by underground or overhead conductors installed and/or maintained under the exclusive control of utilities (including their authorized contractors or other qualified persons).
5. Utility facilities and functions on the line side of the service point located on public or private property in accordance with legally established easements or rights-of-way, contracts, other agreements (written or by conditions of service), or as authorized by a regulating or controlling body.
...
8. Similar systems to those listed above that are under the exclusive control of qualified persons and authorized by a regulating or controlling body, including those associated with an industrial complex or utility interactive system.
B. Not Covered
NESC rules do not cover:
1. Utilization equipment or premises wiring located beyond utility service points to buildings or outdoor installations, or
2. Underground mine wiring or installations in ships, railway rolling equipment, aircraft, or automotive equipment, or
3. Luminaires not installed or maintained under exclusive control by utilities, or
4. Industrial complex or utility interactive systems that are not controlled exclusively under utilities or qualified persons or are located on the premises wiring side of the service point.
So, if the lights are installed and/or maintained by the utility and connected to the utility system and not to the customer equipment, that is under the NESC. Luminaires beyond the service point are under the NEC.