Why is that much different than some low volt services?We have a 12.47KV 3-Ph service. The order of items are in following order:
0: POCO side
1: service point
2: air switch
3: fuses
4: metering PTs and CTs
5: a line leading to our pole pigs and pad transformers with associated air switches and cutouts.
Strangest layout I've ever seen for a service point.
call Gary Gonzales at SCE 909-548-7051 and he may be able to shed some light on it for you or may know of someone you can talk to.
BecauseWhy is that much different than some low volt services?
0: POCO side
1:service point
2:service raceway
3: meter disconnect
4: self contained meter & socket
5: customer raceway/cable and/or service disconnect
Everything on customer side of service point is customer owned and their responsibility to maintain, with exception that any metering equipment within the meter socket or CT cabinet is POCO controlled and likely is POCO owned.
2 and 3 are the true/legal service disconnect, not exclusively the "meter disconnect".0: POCO side
1: service point
2: air switch
3: fuses
4: metering PTs and CTs
5: a line leading to our pole pigs and pad transformers with associated air switches and cutouts.
Because
2 and 3 are the true/legal service disconnect, not exclusively the "meter disconnect".
[We treat the secondaries of transformers as thought they were "service entrances" because they have the same characteristics as a POCO distribution transformer secondary (no overcurrent protection until building main CB, and very high available fault currents.]