Hello I just need a quick sanity check on this.
When looking at an existing building sometimes we are lucky enough to get utility bill which include both the kWH and kW for the service. As far as I know, the peak kW*1.25 is what in calculations for the existing loads per 220.87.
Is there anything that kWH is used to determine other than consumption? I've seen some calculations where people assume some peak hours and intervals days then use that to extrapolate to a kW value larger than what the utility peak demand is calling for. I don't see any example calculations in the NEC for it so I'm just curious if I'm missing something.
When looking at an existing building sometimes we are lucky enough to get utility bill which include both the kWH and kW for the service. As far as I know, the peak kW*1.25 is what in calculations for the existing loads per 220.87.
Is there anything that kWH is used to determine other than consumption? I've seen some calculations where people assume some peak hours and intervals days then use that to extrapolate to a kW value larger than what the utility peak demand is calling for. I don't see any example calculations in the NEC for it so I'm just curious if I'm missing something.