drcampbell
Senior Member
- Location
- The Motor City, Michigan USA
- Occupation
- Registered Professional Engineer
... Why would a meter reset every 15 mins if the max demand charge is for a whole billing period? Wouldn't the only reason be because it measures demand as kWh consumed over a 15min interval? ...
It would be resetting its internal interval timer, not its kW or kWh accumulator.
A likely algorithm:
Each time the second hand advances from :59 to :00:
- Look at the kWh accumulated over the past 15 minutes.
- If it's more than the previous maximum value, make it the new maximum value.
At the end of each month: (billing period)
- Fetch the maximum number of kWhr accumulated during any 15-minute period, multiply by 4, and report that as the maximum kW demand for the month.
- Reset the kWh accumulator to zero.
The peak billing kW concept is motivated by how many more-costly generators the POCO needs to maintain in reserve and bring on line for short periods of time, (a few hours at a time) not by instantaneous motor-starting inrush currents.