But if a load of 1,220 persisted for 15 mins on a 2000A breaker I would be very impressed that the wire is still in solid. Its worth noting that there was an Siemens Energy meter that measured the maximum demand load as 350 kW. The building doesn't have any outages or breaker trips so that's why I'm dubious about trusting the 1,220 number.
@JoeStillman & @ron In post #8 by "ratcheted" value do you mean that they pad the number out based on demand loads for that month? I pretty sure I understand what you are saying but the next month the Billed and Measured demand are the same number at 239.8 kW.
So are you saying that between 239.8 kW and 280 kW there is a service change were they round up just charge you for 1220 kW because its the next size up?
You're right, that is too much for a 208V service and surely would have tripped the main. How many months did the 1220 show up on the bills?
Yes, I meant exactly what you said about "ratcheted". They pad out the bill because of the infrastructure that the utility has to have to supply that many watts. Here in PA, you have "contract minimum and maximum demand" with the utility - the amount that the POCO agrees to build capacity for. If your minimum demand is 1220 kW and your metered 15 minute peak is 280 kW, you would pay for 1220 - and request a new contract!
I would call the utility and ask them to explain the anomoly.