fastline
Senior Member
- Location
- midwest usa
- Occupation
- Engineer
Met with the utility guys today for a 400A 240/120 service. I was trying to avoid them adding a utility easement in the middle of my property (which they have right to access) but my secondary distance was getting expensive at 300ft. I think we will have no choice but to run the primary closer to the structure.
I have more than enough loads to justify the 400A and will certainly use it but I am getting the option on transformer sizing, however I get to pay for it....
They then charge $/KVA minimums against the transformer size.
I know utilities way under size transformers, which is fine, as long as I don't have issues. He said they will replace it if blown up. As it stands, I was probably leaning at 100KVA and he was at 50KVA, but we might negociate at 75KVA. Most of my loads are motor loads so PF considerations should be considered I think.
So what kind of head room do these pad mount transformers really have?
Also, wading into thick water but they put a limit of 10HP for motors on the single phase line but will give me all the amps I want. I realize they are trying to consider inrush on motor starts but I am curious how sticky this can get when I run bigger motors on VFDs? Pretty much my machines are 15-20HP but with about a 2-4sec spool up time. I run a bank of 10HP motors and caps to make a balanced 3PH bank. My inrush would be limited but not uncommon for my machines to go from min to max loads a few times/minute.
Across the line starts can be 10x the name plate current for starts but VFDs are usually limited to no more than 150% of rated continuous current for acceleration. I guess I am basing some of this on that fact to consider what I might reasonable be able to run without a call from them....
I have more than enough loads to justify the 400A and will certainly use it but I am getting the option on transformer sizing, however I get to pay for it....
I know utilities way under size transformers, which is fine, as long as I don't have issues. He said they will replace it if blown up. As it stands, I was probably leaning at 100KVA and he was at 50KVA, but we might negociate at 75KVA. Most of my loads are motor loads so PF considerations should be considered I think.
So what kind of head room do these pad mount transformers really have?
Also, wading into thick water but they put a limit of 10HP for motors on the single phase line but will give me all the amps I want. I realize they are trying to consider inrush on motor starts but I am curious how sticky this can get when I run bigger motors on VFDs? Pretty much my machines are 15-20HP but with about a 2-4sec spool up time. I run a bank of 10HP motors and caps to make a balanced 3PH bank. My inrush would be limited but not uncommon for my machines to go from min to max loads a few times/minute.
Across the line starts can be 10x the name plate current for starts but VFDs are usually limited to no more than 150% of rated continuous current for acceleration. I guess I am basing some of this on that fact to consider what I might reasonable be able to run without a call from them....