This is a rural area so there is otherwise no easements with private water well and septic. I agree on the 'utility' easement regarding who can enter but I guess I don't like people having authority to access. However, again, this is a rural area I doubt they will have some interest is making camp in my yard and the underground utility means they won't be in to repair poles, ever....![Smile :) :)](data:image/gif;base64,R0lGODlhAQABAIAAAAAAAP///yH5BAEAAAAALAAAAAABAAEAAAIBRAA7)
Regarding the loads, I will have my own transformer but yes, from what I gather, they are primarily looking at how my draw affects others power quality. They are pretty blunt and fixed on this '10hp rule' so I gave up trying to reason with them and will do it anyway. Makes no sense that they will give me as many amps as I want, but limit the motor sizes.
Per the POCO engineer, they had issues with a customer starting a 20hp RPC before. Don't know the specifics on that but I suspect that was on a shared transformer..... The biggest question is what that primary line will be doing when I drop something across-the-line.
Regarding the loads, I will have my own transformer but yes, from what I gather, they are primarily looking at how my draw affects others power quality. They are pretty blunt and fixed on this '10hp rule' so I gave up trying to reason with them and will do it anyway. Makes no sense that they will give me as many amps as I want, but limit the motor sizes.
Per the POCO engineer, they had issues with a customer starting a 20hp RPC before. Don't know the specifics on that but I suspect that was on a shared transformer..... The biggest question is what that primary line will be doing when I drop something across-the-line.