Utility Voltage Tolerance

Status
Not open for further replies.
I believe that tolerance is set by your states public service commission. In Illinois the Illinois Commerce Commission has set the voltage range at 113 to 127 for a nominal 120 volt system and plus or minus 10% for all other voltage systems.
 
I must use this opportunity to point out that everyone should pay close attention to the order in which the voltages are stated within the standard; as this has been a contested (testy) issue for some.:grin:
 