I have a bath vanity that will be 6" from the shower/tub . I dont usually have the vanity by the tub that way . I am wondering about the the vanity lights if I put the single lights on each side of the mirrow like I wanted ,one will be right by the tub . If I use the light over the mirrow in the center the edge of light will still be 12" or so from the tub and approx 6 ft high. Isnt there something in the code about the lights have to be 36" from the tub edge ?
 

jetlag

Senior Member
Thanks bphgravity

Thanks bphgravity

The section in the code you want to review is 410.10(A) and (D). NEC 2008 edition.

Thanks for reply . Exhibit 410.1 in the NEC 08 handbook makes it all clear , it seems the securely fastened wall lights or flush or recessed ceiling lights are allowed in the 3 ft zone and dont have to be listed as damp or wet if not directly over the tub.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Jetlag, Violation or not?


ry%3D480
 

jetlag

Senior Member
Jetlag, Violation or not?


ry%3D480

The way I understand it that is not a violation since the fixtures are securely mounted, but being directly over the tub they must be listed for damp location , and it doesnt look like that kind of fixture , If there was a shower the lights would need to be listed wet location . what I dont understand is why there is not a heigth limit for the wall mounts , how could a wall light 1 ft above the tub only need to be for damp location ?
 
Last edited:

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
The way I understand it that is not a violation since the fixtures are securely mounted, but being directly over the tub they must be listed for damp location , and it doesnt look like that kind of fixture , If there was a shower the lights would need to be listed wet location .

Close. No shower then it does not need to be listed for damp location. I see nothing wrong with this install.
 

jetlag

Senior Member
Thanks dennis

Thanks dennis

Close. No shower then it does not need to be listed for damp location. I see nothing wrong with this install.

Doesn't the end of 410.10 D say those lights less than 8 ft directly above the tub have to be listed damp and if subject to shower spray they must be listed for wet ?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Doesn't the end of 410.10 D say those lights less than 8 ft directly above the tub have to be listed damp and if subject to shower spray they must be listed for wet ?

I am sorry correct you are. I wasn't thinking straight-- those fixtures, as I was told are rated for damp location. If it is over 8 feet from the rim then it doesn't have to be damp location rated.
 

jetlag

Senior Member
thanks dennis

thanks dennis

I am sorry correct you are. I wasn't thinking straight-- those fixtures, as I was told are rated for damp location. If it is over 8 feet from the rim then it doesn't have to be damp location rated.

I never thought I would see the day you had to make a correction , It does not happen often , you are the code wizzard :grin: Do you have an answer why they dont give a min. height for the fixtures only rated damp inside the tub restricted area directly over the tub ? :confused:
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I never thought I would see the day you had to make a correction , It does not happen often , you are the code wizzard :grin:
You give me way too much credit-- my brain is half asleep most of the time.:)
Do you have an answer why they dont give a min. height for the fixtures only rated damp inside the tub restricted area directly over the tub ? :confused:
I suppose they don't see an issue with it. Personally I think it is a bad install which I have done at the ho request-- "Hey honey hand me a bulb, I am taking a bath and the darn thing just burn out."
 

infinity

Moderator
Staff member
Location
New Jersey
Occupation
Journeyman Electrician
I have a bath vanity that will be 6" from the shower/tub . I dont usually have the vanity by the tub that way . I am wondering about the the vanity lights if I put the single lights on each side of the mirrow like I wanted ,one will be right by the tub . If I use the light over the mirrow in the center the edge of light will still be 12" or so from the tub and approx 6 ft high. Isnt there something in the code about the lights have to be 36" from the tub edge ?

What code cycle are you under?
 

jetlag

Senior Member
You give me way too much credit-- my brain is half asleep most of the time.:)

I suppose they don't see an issue with it. Personally I think it is a bad install which I have done at the ho request-- "Hey honey hand me a bulb, I am taking a bath and the darn thing just burn out."

Thats not as bad as me years ago I let an HO talk me into putting a small ceiling fan over a tub at his wife's command . It had a ten foot ceiling so my brain quit working and I was thinking 8 ' above the floor . Didnt think untill I got home the 8 ft is above the tub rim . Its been 4 years and I worry to this day that something will go wrong. It even has a pull chain they can reach :confused:
 

jetlag

Senior Member
You give me way too much credit-- my brain is half asleep most of the time.:)

I suppose they don't see an issue with it. Personally I think it is a bad install which I have done at the ho request-- "Hey honey hand me a bulb, I am taking a bath and the darn thing just burn out."

In a case like you had , I think the bulb should be completely enclosed and on a GFCI circuit and installed at least 7 ft above the tub bottom , that way they have to make more effort to contact the bulb socket . They dont allow things like that in a hot tub , but then they probably figure a good chance people will be hitting the booze :grin:
 
In a case like you had , I think the bulb should be completely enclosed and on a GFCI circuit and installed at least 7 ft above the tub bottom , that way they have to make more effort to contact the bulb socket . They dont allow things like that in a hot tub , but then they probably figure a good chance people will be hitting the booze :grin:

A GFCI will not protect one if the person gets between the ungrounded and grounded conductor.


BTW: that is why I hand my wife the bulb:D:D;):cool:
 