- Location
- Mission Viejo, CA
- Occupation
- Professional Electrical Engineer
Why would you need gas detection in an otherwise unclassified location?
rbalex said:Why would you need gas detection in an otherwise unclassified location?
rbalex said:Think about it this way, in the world of Documents API RP 500 is neither a Code nor Standard. It is a Recommended Practice. It does have benefit of ANSI sanction which will generally give it a sound footing when used as a design basis. However, if there is an interpretive conflict between NEC Section 500.7(K) (1) which says you are permitted to use Division 2 methods in a Division 1 location and API RP 500 Section 6.5.1 which says you can actually reclassify it as Division 2 ? which do you think would win in a court?
I certainly see your point, but if RP500 is a basis for determining Classification as used in NEC 500, how can RP500 6.5.1 be selectively disqualified?
I was on CMP 14 when gas detection became a permitted protection technique. I wasn?t so much opposed to it as simply saying the guidelines weren?t sufficient. This was my ?affirmative? comment on the Panel Action:
I wish you would have been successful... it would really help to have a better explanation.
Now a rephrase of my earlier question: Why would you have a gas detector if you didn?t expect there to be a possibility of gas to detect? If there is a possibility of gas, what does it imply about the electrical area classification. Hint: See Section 500.5(B)
Edit: Added the API Section number in the opening paragraph
It is much clearer, there would be no need for Gas Detection in an unclassified area. The presence of Gas Detection would imply a Div.2 area.
Because it doesn't always conform to the NEC, although it intends to. As I said earlier, some of the non-conforming applications are accepted by the US Coast Guard. Then it's the NEC that doesn't apply.stickelec said:I certainly see your point, but if RP500 is a basis for determining Classification as used in NEC 500, how can RP500 6.5.1 be selectively disqualified?
...
Almost got it - it implies a Class I location. It may be either Division 1 or 2. (Assuming it is detecting an ignitible gas, of course. E.g., it could be an oxygen or nitrogen detector. They each have their own safety issues, they just don't cause Classified locations.)stickelec said:...It is much clearer, there would be no need for Gas Detection in an unclassified area. The presence of Gas Detection would imply a Div.2 area.
rbalex said:Because it doesn't always conform to the NEC, although it intends to. As I said earlier, some of the non-conforming applications are accepted by the US Coast Guard. Then it's the NEC that doesn't apply.
rbalex said:I wouldn?t call educated judgment ?subjective.?
I didn't mean it to be derogatory at all. In my own experience, and others that I have oberved on this forum, there is more than one interpretation (or viewpoint) even from Engineers.
The NEC isn?t ??a design specification or an instruction manual for untrained persons.? (Section 90.1(C)) The key is becoming familiar enough with the subject matter to recognize what material does and doesn?t apply and when and where it applies.
I'm not sure where we are going with this one, but I'll be the first to admit I don't know it all and am still learning, I have been in the Industrial side of this business for over 30 years however.
As ?Recommended Practices? API RP 500 and NFPA 497 essentially ARE design manuals, but they DON?T necessarily apply in every case and they are still not for ?untrained persons? either. You must recognize when they apply. That is where experience comes in.
"Recognizing where they apply and don't apply"... that is the question for me at least. But, your time and expertiece has helped tremendously.
One of the problems with RP 500 is that it hasn't been updated since the NEC recognized a limited use of gas detection. I also wish the gas detector industry (the originators of the Proposal/Comment that was accepted) would have taken the advice to develop more comprehensive guidance. If you read their original Proposal they wanted gas detection to be a general purpose solution. After reading the "acceptable" applications in RP 500, I?m sure you know they aren't general purpose solutions. Some gas detector manufactures are still marketing their products that that way though. So caveat emptor.
Understood.
As we have noted, the NEC doesn?t apply everywhere either ? but it probably applies to your installation. Since it does, except for the very limited application of Section 500.7(K)(1), gas detection doesn?t change the electrical area classification but ?n a Class I, Division 1 location that is so classified due to inadequate ventilation, electrical equipment suitable for Class I, Division 2 locations shall be permitted.? That isn?t subjective at all.
Thank you very much. As you can probably tell, I have been "in the books" since early this morning trying to gain a better understanding. Thanks again for your time.
I hope I can still have an opportunity to request a few more bits of information on this subject as time goes on.
As we have noted, the NEC doesn?t apply everywhere either ? but it probably applies to your installation. Since it does, except for the very limited application of Section 500.7(K)(1), gas detection doesn?t change the electrical area classification but ?n a Class I, Division 1 location that is so classified due to inadequate ventilation, electrical equipment suitable for Class I, Division 2 locations shall be permitted.? That isn?t subjective at all.
Please clarify the question if I?m not interpreting it correctly.stickelec said:I wasn't going to pursue this any further but this one bothered me all night, so if I could please...
Per 500.7(K)(1) I can have the following:
a) Compressor Building classified Div.1 due to Inadequate Ventilation.
b) Combustible Gas Detection present.
c) Equipment and Wiring Methods consistant with Div.2 requirements.
Why do I have a Div.1 building, nothing inside is to Div.1 specification?
It looks like an easy out to just classify Div.1 and not go to the trouble to meet the requirements for Adequate Ventilation. As was mentioned earlier, DOT mandates Gas Detection anyway (in our application).
rbalex said:Please clarify the question if I?m not interpreting it correctly.
To begin with, from the OP I believe we are talking about methane, a lighter than air flammable gas. Since you have RP 500 available now, we start with two basic options ? see Section 9.2.2.2 with its accompanying figures 25 and 26, both on page 35. From what I have understood so far, Figure 26 is the more applicable. Therefore, with no other information and forgetting gas detection and DOT for the time being the interior of the building would be Class I, Division 1.
My application is a Compressor Building as illustrated in Figure 25... but yes it would be Div.1 as you described.
Now let?s add the DOT requirements ? they are irrelevant for the classification analysis. They are provided for personnel warning and the electrical area classification doesn?t change. The installation still needs to be suitable for Division 1.
Understood
Next let?s add gas detection that conforms to API RP 500 Section 6.5.1a. We must also recognize that Section 6.5.1b is not applicable because the location under discussion DOES ??contain a source of flammable gas or vapor?? The rest of Section 6.5.1b is irrelevant for the discussion.
Agreed
Section 6.5.1a then leads us Section 6.5.2. If you then follow all the instructions in Section 6.5.2, Section 6.5.1a says you may treat the location as Division 2. NEC Section 500.7(K)(1) says you are permitted to use Division 2 methods. For most practical cases it is the same thing
This was the part that was hard to grasp...
We can have a Compressor Building with Inadequate Ventilation if Gas Detection is present per 6.5.2. However, the NEC does require it be classified Div.1 but Div.1 equipment is not necessary. The whole ventilation thing sort of goes out the window.
I think the "unwritten piece" I may be missing is the whole effort to classify Div.1 is just to be sure the Gas Detection requirements are an integral part of the overall classification documents and drawings.
rbalex said:That?s interesting ? I had the impression that the compressor building was totally enclosed. If it is more like Figure 25, why are you worrying about ventilation? After you install the DOT required gas detectors the only real concern would be lighting and possibly an overhead crane; neither of which could economically justify additional gas detection.
rbalex said:Figure 26 applies. Figure 25 is a "shelter" - open bottom, enclosed (inadequately ventilated) top. You didn't notice it was Division 2 around the "source?"
stickelec said:Ok my bad. I just wasn't expecting an enclosed Compressor Building (Shelter) with enclosed top, sides, and bottom that doesn't have the "source" inside.
Point is, if we add either Ventilation or Gas Detection inside the Div.1 enclosed area we could use Div.2 equipment.
weressl said:Hm......
Open bottom compressor shelters are usually constructed with a top venting ridge that will allow lighter-than-air gases to escape. That COULD constitute adequate ventillation. That construction style was developed just for that reason.
KentAT said:Stickelec - Is your compressor building part of a natural gas pipeline facility?
Kent, the compressors are Natural Gas Compressors, typically there are at least three in a building. And yes, section 14 is applicable, there?s just a lot of math there.
I probably shouldn?t even be exploring this subject? I?m not an engineer or an expert in design of an area classification. But, a number of years ago I went through a similar ordeal as you, my company changed all compressor buildings from Div.1 to Div.2. One day they were Div.1 the next day they were Div.2, nothing changed.
In those days I just accepted it for one reason? lack of information on my part. Not that I could have done anything about it.
So, I began to study and study a lot. I was also fortunate enough to find this forum which has helped tremendously.
Now, back to the subject at hand. If we?re going to live with these Div.2 buildings, I think Adequate Ventilation (by definition) is the key?if the correct safety response occurs in case of failure. Gas detection is also an asset and required in our application by DOT as you pointed out.
What really has my head spinning is if Gas Detection is utilized per RP500 6.5.2, then NEC Article 500.7(K)(1) disqualifies any requirement for ventilation. It states: ?In a Class 1, Division 1 location that is so classified due to inadequate ventilation, electrical equipment suitable for Class 1, Division 2 locations shall be permitted.?
It looks to me like if the paper says Div.1, then forget the fans, forget Div.1 wiring methods, we have to have Gas Detection anyway, so all is okay. I?ve probably missed it again? but I?m trying to get this clear in my head.