For the partially enclosed issues. re-look at 6.3.2.4.7.
Simplified Div. 2 cirteria: Inadequatley ventilated, with adequate gas detection = Div. 2. See 6.5.1a. Technically non-ventilated space is OK with adequate gas detection, however nuisance trips will cause management to ask you to jumper out the trips, thus adequate gas detection is compromised.
Kent, RE your statment about declassifying to Div. 2 because the equipment didn't meet Div. 1. Be very careful. Classification comes first. Equipment must meet the classification. Do not reverse these. I remember about 15 years ago, a pipeline that shall remain nameless was fined heavily by OSHA for adjusting the classification to meet the equipment.
You probably have problems with ignition systems, coils, and spark plug wiring that are not shileded, Div. 2 approved. Typically I have heard compressor mechanics like to swap out shielded, Div. 2 coils to the non-approved, unshielded types because it's easioer for them to start-up the machines. Not good......
Bottom line, get the gas detection and alarms and shutdowns correct so you can justify Div. 2.
Simplified Div. 2 cirteria: Inadequatley ventilated, with adequate gas detection = Div. 2. See 6.5.1a. Technically non-ventilated space is OK with adequate gas detection, however nuisance trips will cause management to ask you to jumper out the trips, thus adequate gas detection is compromised.
Kent, RE your statment about declassifying to Div. 2 because the equipment didn't meet Div. 1. Be very careful. Classification comes first. Equipment must meet the classification. Do not reverse these. I remember about 15 years ago, a pipeline that shall remain nameless was fined heavily by OSHA for adjusting the classification to meet the equipment.
You probably have problems with ignition systems, coils, and spark plug wiring that are not shileded, Div. 2 approved. Typically I have heard compressor mechanics like to swap out shielded, Div. 2 coils to the non-approved, unshielded types because it's easioer for them to start-up the machines. Not good......
Bottom line, get the gas detection and alarms and shutdowns correct so you can justify Div. 2.