I'm working on installing a 300hp VFD for one of our vertical Well Pump motors...is this a constant torque or variable torque application? Please advise, thanks
Most likely variable. All the ones I've done have been. But note what kwired posted.All,
I'm working on installing a 300hp VFD for one of our vertical Well Pump motors...is this a constant torque or variable torque application? Please advise, thanks
300hp VFDis the drive modulated or running at a constant speed once started?
300hp VFD
we used vfd's, to limit inrush current, but the sewage pumps always ran at full speed
they were not much more expensive than a SS, but offered more flexibility
our utility REQUIRED anything over 25 HP to have a vfd (or SS), even for constant speed application
best to include the whole post rather than selectively edit and highlight to demean someone
Ingenieuris the pumping rate constant? head and gpm?
is the drive modulated or running at a constant speed once started?
[/INDENT]We are planning on varying the frequency on this drive, in the past we started it across-the-line and ran it at a full 60 Hz all the time. I'm in an industrial plant, if we used a VFD for everything above 25hp we'd be broke haha. I believe we're trying to change the pumping rate with this VFD.
The question was CT or VT. That has been answered.we used vfd's, to limit inrush current, but the sewage pumps always ran at full speed
they were not much more expensive than a SS, but offered more flexibility
our utility REQUIRED anything over 25 HP to have a vfd (or SS), even for constant speed application
best to include the whole post rather than selectively edit and highlight to demean someone
Ingenieuris the pumping rate constant? head and gpm?
is the drive modulated or running at a constant speed once started?
the requirement applied if you took service at 480 vac or less (which we always did for remote pumping sites)
you probably take it much higher
you app is variable torque then
but honestly, iffy, say if you change the speed once a year, then fixed for long periods, versus a controller constant varying speed under changing head conditions
either way, safe with variable torque
Yes, but that would probably be of more significance for the motor.You should coordinate this with pump motor mfr and drive mfr. A lot of special requirements for deep submersibles with VFD. Notably ramp up/down times for porpoer cooling and OL protection.
femyers.com/~/media/websites/myers/sellsheets/48150.pdf
Yes, but that would probably be of more significance for the motor.
A little tale. And something the OP ought to be aware of. I was called to a site where the motors on submersible pumps with VFDs were failing at the rate of about one a month. To keep it brief, the cause was excessive dv/dt. Rate of change of voltage. Over 3000V/us in some cases. A killer if not taken care of at the project design phase.
Output chokes was the fix. Not all VSD come with them.
Constant v/f is the way I would go. Reducing the v/f ought to reduce losses. I tried that on some 630kW pump drives. Test results were inconclusive and introduced other problems so we reverted to constant v/f open loop.I've taken note and installed both line and load reactors. I guess my question then is what control method would be best for this application, since we're varying speed based on plant header PSI, V/Hz or open loop? Since it's varying torque you'd think open loop right? From my understanding V/Hz is for constant torque applications.
The question was CT or VT. That has been answered.
Spare the irrelevant clutter. OK?
I've taken note and installed both line and load reactors. I guess my question then is what control method would be best for this application, since we're varying speed based on plant header PSI, V/Hz or open loop? Since it's varying torque you'd think open loop right? From my understanding V/Hz is for constant torque applications.
v/f since you do not need low f high torque capability
since you have closed loop PID control the drift will not be an issue
we use open loop vector for tensioning winch applications
when you need max torque at <0.3 Hz
the motor is essentially stationary ~ +/- a few tenths Hz
One thing I do want to point out, is that the PID loop isn't set up inside the VFD, but rather in our PLC.